13-07-2010, 03:03 AM #1
oversizing condenser fan motors?
1/4 horse 1075 condenser fan motor replaced by a 1/2 condenser fan motor, does this pose a problem by spinning faster due to pitch of fan? i would like to think that this could cause over condensing problems. am i correct or am i wrong?
-
13-07-2010, 04:57 AM #2
Re: oversizing condenser fan motors?
Why does the fan spin faster! (excluding slippage) HP is not related to speed.
-
13-07-2010, 07:08 AM #3
Re: oversizing condenser fan motors?
Speed in AC motors is related to the number of poles in the motor.
2 pole motor at 50HZ has nominal speed of 2800 RPM
4 pole motor at 50HZ has nominal speed of 1400 RPM
6 pole motor at 50HZ has nominal speed of 900 RPM.
These nominal speeds are a little less than the Synchronous speed due to slip.
It is worth mentioning that most small condenser fan motors on packaged units are Shaded Pole
-
13-07-2010, 01:29 PM #4
-
13-07-2010, 02:03 PM #5
Re: oversizing condenser fan motors?
high power consumption using a 1/2 hp motors,a costly replacement.why not replace the original.
abet
-
13-07-2010, 02:20 PM #6
Re: oversizing condenser fan motors?
Maybe they don't have in stock for fast delivery. The higher consumption should not be very high because the fan is the same so the shaft power absorbed should be nearly the same...and maybe this bigger motor maybe have a higher efficiency, even at part load.
To make progress is never good enough, I want to do better and better and better
Similar Threads
-
oversizing condenser fan motors?
By delta T in forum ElectricalReplies: 3Last Post: 14-07-2010, 04:58 AM -
Parallel condensers Shell and tube paralle with Evaporative Condenser
By Herschmidt in forum NH3Replies: 2Last Post: 08-06-2010, 11:12 PM -
How to measure COP (evaporative condenser)
By Juho in forum Technical DiscussionsReplies: 5Last Post: 04-06-2010, 07:08 PM -
Evaporative Condenser system COP
By Juho in forum CommercialReplies: 0Last Post: 03-06-2010, 09:23 AM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM