Results 1 to 3 of 3
Thread: load calculation
-
12-07-2010, 05:59 AM #1
load calculation
Can you please help me calculate refrigeration load for 200,000 litres per day milk plant? Kindly give me a step by step calculation.
-
12-07-2010, 06:35 AM #2
Re: load calculation
Hi there,
You did not mention the time requirement. Usually dairy companies receive a huge amount of milk everyday and it must be cooled very quickly say 1 hour. For this reason every company has an ice storage system. This means a relatively small refrigeration system works for 24 hours and produces ice around evaporator tubes. Then the latent heat of ice is used to cool the milk in a short time. This is called ICE BANK.
About the load : m x Cp X DT = Q
where :
m is the mass flow rate of the fluid to be cooled in kg/s
Cp is the specific heat of the fluid in kJ/kg°K
DT is the temperature difference in °C
Q = (200000/24*60*60)*3.7*(30-2) =2.31*3.7*28 = 239 kW
(assuming that milk density is 1000kg/m³ like water. Means 1 liter of milk equals one kg.)
CheersEven Einstein Asked Questions
-
12-07-2010, 03:52 PM #3
Re: load calculation
just a correction, despite the final result is correct:
» (200000/(24*60*60))*3.7*(30-2)
time in seconds for cooling (S.I. units) » 24hours*60min*60secondsTo make progress is never good enough, I want to do better and better and better
Similar Threads
-
Cooling load calculation
By naveenvm in forum FundamentalsReplies: 19Last Post: 22-07-2011, 05:44 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Cooling Load Calculation
By jervame_sireh in forum FundamentalsReplies: 0Last Post: 21-04-2007, 11:05 PM -
Cooling load calculation
By raviperumal in forum Technical DiscussionsReplies: 6Last Post: 02-03-2007, 04:09 AM