Undercharged vrv system symptoms?!??
Hi guys
Have a vrv system this is not cooling rooms down but showing no faults.
Have been lead to believe that the additional charge to be incorrect by around 5kg! System runs and completes quick wiring and pipeing test with no problems.
Any advice would be much appreciated. Many thanks
-
30-06-2010, 09:52 PM #2
Re: Undercharged vrv system symptoms?!??
What's SH on the indoor unit the most far away for the outdoor unit after switching on all the indoor units in continuous cooling mode (set to 17°C)?
Have you used a Service Checker? It can give you the readings of all the probes.
Recover everything, weight and recharge correctLast edited by Peter_1; 01-07-2010 at 07:59 AM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-07-2010, 07:41 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Undercharged vrv system symptoms?!??
Fastest solution is recover and weigh proper charge after verifying what correct charge should be by checking pipe lengths and instalation manual.
-
01-07-2010, 08:57 AM #4
Re: Undercharged vrv system symptoms?!??
It's a water cooled vrv with 30 degree water supply in.
Was getting around 15 bar suction in full cooling. With room temps of 26 plus. And remotes set to 16 degrees we get air off 22 degrees at best.
It's a heat recovery 3 pipe
Affraid no service checker.
-
01-07-2010, 05:24 PM #5
Re: Undercharged vrv system symptoms?!??
Some electric valve is open when it should be closed?
Stuck 4way valve?
-
01-07-2010, 06:02 PM #6
Re: Undercharged vrv system symptoms?!??
is 30degree water in too high? is it daikin vrv or other vrf? R410a presumably at the pressures given, why do you suspect an undercharge?
Alec
-
01-07-2010, 06:29 PM #7
Re: Undercharged vrv system symptoms?!??
More like over indexed than undercharged...
-
02-07-2010, 09:37 AM #8
Re: Undercharged vrv system symptoms?!??
Check out page 76 on here
http://www.heronridge.co.uk/falt_cod...20training.pdf
-
04-07-2010, 10:23 AM #9
Re: Undercharged vrv system symptoms?!??
about thermistors? i thought that at first as the indoor units are in the mezz space 32 degree air on and duct into the air conditioned space.
it has a centralized controller which is showing the room temps at around 26/30 degree's so the condensing units must know that they are being asked for cooling.
There are 2 x condenser linked together and the slave seems to be the one doing all the work ie master compressor doesnt run. But is getting very very hot. altough it isnt on and pumping (not drawing amps) is has a liquid discharge off 34bar still.
the slave unit is producing 15bar suction pressure and 33 bar liquid. with indoor air off temps of no better than 20 degress when in full cooling.
any ideas guys? when should to compressors cut in and out?
and under full load they would both run wouldnt they?
many thanks
-
04-07-2010, 06:03 PM #10
Re: Undercharged vrv system symptoms?!??
3 way valve problem maybe?
Many thanks
-
04-07-2010, 08:10 PM #11
Re: Undercharged vrv system symptoms?!??
If it's undercharged the compressors can run with high discharge temps.
If the system detects its running out of parameters the comps may be unloaded to safegaurd against damage.
If you post the model no. of your units you'll probably get better info specific to your system..
There's loads of posts on here re the performance of VRV's, have a search..
I don't think your system is a Mits Elec but here's one recent post-
http://www.refrigeration-engineer.co...ad.php?t=25318Last edited by Gingerair; 04-07-2010 at 08:26 PM. Reason: Lads & dads...
-
04-07-2010, 08:41 PM #12
Re: Undercharged vrv system symptoms?!??
Sorry it's a Daikin water cooled...
-
04-07-2010, 09:01 PM #13
Re: Undercharged vrv system symptoms?!??
Hi Alec, you got a year & model No. ???
Last edited by Gingerair; 04-07-2010 at 09:03 PM.
-
04-07-2010, 09:55 PM #14
Re: Undercharged vrv system symptoms?!??
Hi Alec,
Are you sure the master module has not been disabled via the outdoor unit pcb (field setting - mode 2 setting 38 )? This would prevent the master unit operating.
A liquid line pressure of 33 bar is excessively high, I suspect you have insufficient water flow through the condenser plate heat exchangers.
Have you checked the following:
1/ Head pressure (should be <30bar – limiting function will be active >29.5bar)
2/ Entering/leaving water temperatures (difference should be < 10 C)
3/ Water flow rate (nominal flow rate is around 90 l/min per unit)
Each unit should have an inlet water strainer and a flow switch connected across terminal Block X2 connections 3 & 4. I would suggest you check all water strainers and correct operation of the master unit flow switch this could also prevent the master unit operating.Last edited by VRVIII; 04-07-2010 at 10:55 PM.
-
04-07-2010, 10:43 PM #15
Re: Undercharged vrv system symptoms?!??
alec
as per post 6 is your evaporative condenser ok?
al
-
04-07-2010, 11:00 PM #16
-
05-07-2010, 12:15 AM #17
Re: Undercharged vrv system symptoms?!??
you gotta have a sense of humour!!
It's like a customer ringing up, i have a cold room, it's white and not cooling, fix it over the phone for me!
more info would be great.
al
-
07-07-2010, 09:35 PM #18
Re: Undercharged vrv system symptoms?!??
Master Compressor runs in test but not when full cooling? Has correct charge! Thermister problem maybe?
-
08-07-2010, 11:05 AM #19
Re: Undercharged vrv system symptoms?!??
Is there somewhere you can check thermistors are Reading correctly? Is there a link or anything? Ie what in volts it means in bar for daikin vrv?
Many thanks
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
How to determine the suitable air-conditioning system
By Terrywarner in forum Air ConditioningReplies: 9Last Post: 15-05-2010, 08:14 PM -
Enthalpy Increasing Buffer System
By Reflexive in forum Technical SpeculationsReplies: 3Last Post: 23-12-2008, 03:18 PM -
Fan model for system optimization
By autt in forum System OptimizationReplies: 8Last Post: 31-03-2007, 05:34 AM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM