Thread: condensate drainage problems
-
27-06-2010, 03:07 PM #1
condensate drainage problems
hello gents, got a ahu thats leaking condensate, this is the situation. condensate from the evap coil wont run down condensate drain line because the supply air fans seems to be pulling on this water and by intrainment depositing it further along the duct work where there is no drainage and so it leaks where it can. what i find is if i turn the supply air fans off water drains quite freely down the condensate drain or the same thing happens if i open the filter asscess hatch down stream of the evap coil. note the problem is not the condensate drainage pipe work. any help would be great.
-
27-06-2010, 03:54 PM #2
Re: condensate drainage problems
Is it a U trap? Maybe its not low enough?
Are the filters clean? Any return air obstruction?
Was it like that from the beginning or is it new problem?
-
27-06-2010, 05:30 PM #3
Re: condensate drainage problems
Few things to check,
Is the coil clean?
As chemi-cool said is the u trap correct?
On the return air ductwork Is there anything else tee'd in to it?
I had this a few weeks back in a restaurant and found they had tee'd into the return ductwork a kitchen dishwasher.The difference between genius and stupidity is that genius has its limits.
Marc
-
27-06-2010, 08:19 PM #4
Re: condensate drainage problems
you need to fit a p trap and fill it with water
-
27-06-2010, 09:27 PM #5
Re: condensate drainage problems
I think if the drain pan is on the sucky side of the fan it needs a p trap (which will need priming), if its on the blowy side it doesn't want one.
-
28-06-2010, 06:29 PM #6
Re: condensate drainage problems
had something like this 2day,ended up the filters were plugged solid and that created a vacum inside the unit,causing the water 2 splash round with the fans goin. replaced the filter mesh and that sorted the problem..
-
28-06-2010, 06:53 PM #7
-
28-06-2010, 10:59 PM #8
Re: condensate drainage problems
Also make sure that the trap is full of water otherwise it will never work.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-06-2010, 09:35 PM #9
Re: condensate drainage problems
thanks for all the responses, the traps and filters are all ok, what i find when system operating is the condensate water in the condensate pan is pulled by the suction of the supply fans to such a degree that the water is kept away from the drainage pipe almost lifted out of the tray. when an access panel is opened up stream then the water flows down the trap quite freely.
-
30-06-2010, 09:50 PM #10
Re: condensate drainage problems
Your trap on the drainage line should be close to the drain pan and at least 150mm deep then the drain should fall away from the trap. If you have a large static pressure on the fan the drain line may need to be larger than 20mm diameter
-
30-06-2010, 10:16 PM #11
Re: condensate drainage problems
You say that traps are OK but they don't seem to be working.
Check the static pressure at the trap inlet and ensure that the trap is deep enough.
Something on the inlet side of the fan is blocked to have increased the suction pressure from what, we assume, was a working drainage system.
Blocked filter, collapsed filter, dirty coil, fire damper dropped, inlet grille damper closed etc.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
02-07-2010, 10:51 PM #12
Re: condensate drainage problems
the evaporator coil did have a carpet layer of dirt which has been clean, thinking about it the coil would really need a deep clean because internally it is still floud to a degree. thanks chaps...
-
04-07-2010, 02:39 PM #13
Re: condensate drainage problems
The Fresh air intake louver will normally have a bird wire screen behind it, which can get clogged up after a while. Maintenance deals with filters but can miss this one.
Might be worth a check if all else looks okay on the suction side of fan.
Similar Threads
-
Carrier 30XA Liquid chiller Problems
By Ed Burris in forum CommercialReplies: 7Last Post: 13-08-2010, 08:12 PM -
Condensate drainage regulations
By topfridgeman in forum Technical DiscussionsReplies: 1Last Post: 04-03-2009, 11:12 PM -
Hartell Condensate Pump
By Grizzly in forum Air ConditioningReplies: 8Last Post: 03-01-2008, 09:08 AM -
Suction pressure problems on TS units at low ambient temps
By nova in forum TransportReplies: 10Last Post: 18-03-2006, 07:35 PM -
Oil return problems
By Peter_1 in forum IndustrialReplies: 37Last Post: 23-08-2004, 11:30 PM