    Hi All,

    The company I work for has recently installed a multiplex plant consisting of 2 x 100kW medium temp and 1 x 36kw low temp (for a mini market). This is the first job of this magnitude where we have gone with electronic expansion valves (not the motorised type).

    The problem we are experiencing is a great amount of liquid hammer, which has never been the case before. My question is, is there a general tendendancy for liquid hammer with the electronic expansion valves, maybe due to the more frequent opening and closing of the valves? What is everybody elses experience with electronic expansion valves an liquid hammer?

    Any advise is most appreciated.



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Liquid Hammer

    What make are the valves?
    Where are they in relation to the evap?
    And is there any form of solenoid valve on the liquid line before the electronic ones? If so how far away from the valve are they?

    Liquid hamer in normaly caused when a valve opens and the liquid runs till it hits somthing solid like an elbow or a valve.

    If the valves are pulsation valves they sould not cause hammer so you need to look to the liquid line and any controling valves in that.

    If you have hammer does the system pump down the cases individualy?


    All the best

    coolrunnings.

    .

  3. #3
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Liquid Hammer

    Liquid hammering (pulsating) could occur in electronic expansion valve systems, like the Danfoss Adap Kool systems.

    Standard practises should be followed in securring all liquid lines tightly on brackets, clamps, etc and to make some form of expansion just before the electronic valve.

    Remember, electronic valves can pulse every second, where normal solenoid valves can open and close every 10 to 15 minutes.

    I hope this will answer your question/point.
    I am not always right, but I'm never wrong!

  4. #4
    Join Date
    Jan 2009
    Location
    UK
    Age
    58
    Posts
    161
    Rep Power
    16

    Re: Liquid Hammer

    Hi Garet,
    If by "liquid hammer" you mean the liquid line bouncing, then with any type of solenoid valve you will get movement when the valve opens but it is more apparent with electronic solenoid operated expansion valves such as Danfoss AKV's because they operate more frequently, up to once every second.
    The obvious answer is to make sure that any pipework is properly secured, although most supermarkets in the UK just rest the pipework on a cushioned bracket and they all use AKV's!

  5. #5
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Liquid Hammer

    Theoretically whatever expansion device u use, liquid hammering shouldn't happen, because the liquid line should be full with liquid, only if you have a solenoid valve that separates the expansion valve from the liquid , the expansion valve lets the liquid pass and gas is formed before the expansion valve and the solenoid valve, and wen the solenoid valve opens, the liquid hammering happens

    fastening of the pipes only reduces the sound effect not the actual hammering that in time damages the components especially the expansion device.

    Whatever expansion device is used if the liquid line is full with liquid not hammering can happen (this doesn't exclude vibrations)

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Liquid Hammer

    Devil, if you stop a fast flowing liquid in a fraction of a second, you will get a huge pressure buildup (hydraulic expansion)
    This is the case with all EEV ' working with the PWM principle.
    Some possibilities to solve: install a T just before the EEV with a piece of copper in the upper part of the T facing up.
    Pre-expansion like a member said.
    Decrease your HP.
    Sure you have 100% liquid at the entrance of the EEV?
    Liquid lines not too small (increased velocity)?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Liquid Hammer

    Generally I have found that with pulsing electronic TX valves the hammer is created by high velocity liquid flows before the TX valve, so by increasing the liquid line size or sub-cooling liquid, effectively reducing the liquid velocity you will stop the hammer effect. The hammer will break something sooner than later. Some thing else to look at is the set up on the electronic TX vavs, the response rates are generally controllable, or can be slowed down.

  8. #8
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Liquid Hammer

    Yes peter, i do agree with you, but if the pipe is properly sized and if you don't have a large portion of pipe going straight and then directly going in the EEV without any bends (because elbows reduce the hammering) you can reduce the hammering eave if you can't exclude it all and yes the T facing up, will allow gas to form in the up part and the gas is compressing eliminating the hammering

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. TEV on long liquid line, liquid hammer
    By Peter_1 in forum Industrial
    Replies: 51
    Last Post: 21-02-2010, 09:37 AM
  3. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •