Hi gentlemen having a problem diagnosing a fault with the above mentioned system.
The runnng suction pressure is approx 45-50psig in cooling mode, the discharge pressure approx 225psig. The compressor is extremely hot and keeps cutting out after approx 30 mins on thermal cut out.
The system is about 10 years old maybe more, air off the duct is 17 degrees c.
The system seems to be running fine as pressures go but not cooling properly.
Any ideas would be greatly accepted.
-
25-06-2010, 09:43 PM #2
Re: LED7 on Mitsubishi Electric PUH4 R22 system
Misti's like to see not less than 0°C on the suction.
Pressures without temperatures do not help too much, check the superheat if the compressor is over heating.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
26-06-2010, 08:47 AM #3
Re: LED7 on Mitsubishi Electric PUH4 R22 system
Debonair Spain,
LED 7 is compressor overheat.sounds like it is short of gas.
I will pm you the manual.
-
26-06-2010, 04:59 PM #4
Re: LED7 on Mitsubishi Electric PUH4 R22 system
Thanks Lawrence 1
-
27-06-2010, 04:31 PM #5
Re: LED7 on Mitsubishi Electric PUH4 R22 system
Does sound like its short of gas, but the pressures seem to be not bad, definatly check the superheat on this unit to check it out
thanks
Similar Threads
-
mitsubishi electric mr slim split type ac
By fish4fun in forum Trouble ShootingReplies: 10Last Post: 30-04-2010, 06:47 AM -
Mitsubishi Electric "replacement setting" on P-Series models
By DL A/C in forum Air ConditioningReplies: 4Last Post: 14-04-2009, 09:42 PM -
Mitsubishi Electric Intermittent fault
By marc5180 in forum Air ConditioningReplies: 28Last Post: 15-01-2009, 10:19 PM -
Mitsubishi Electric VRF
By vijay_study in forum Air ConditioningReplies: 3Last Post: 06-11-2008, 10:03 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM