    LED7 on Mitsubishi Electric PUH4 R22 system



    Hi gentlemen having a problem diagnosing a fault with the above mentioned system.

    The runnng suction pressure is approx 45-50psig in cooling mode, the discharge pressure approx 225psig. The compressor is extremely hot and keeps cutting out after approx 30 mins on thermal cut out.

    The system is about 10 years old maybe more, air off the duct is 17 degrees c.

    The system seems to be running fine as pressures go but not cooling properly.

    Any ideas would be greatly accepted.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: LED7 on Mitsubishi Electric PUH4 R22 system

    Misti's like to see not less than 0°C on the suction.

    Pressures without temperatures do not help too much, check the superheat if the compressor is over heating.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: LED7 on Mitsubishi Electric PUH4 R22 system

    Debonair Spain,
    LED 7 is compressor overheat.sounds like it is short of gas.
    I will pm you the manual.

  4. #4
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    17

    Re: LED7 on Mitsubishi Electric PUH4 R22 system

    Thanks Lawrence 1

  5. #5
    Join Date
    Jun 2010
    Location
    Wales
    Posts
    45
    Rep Power
    0

    Re: LED7 on Mitsubishi Electric PUH4 R22 system

    Does sound like its short of gas, but the pressures seem to be not bad, definatly check the superheat on this unit to check it out

    thanks

Similar Threads

  1. mitsubishi electric mr slim split type ac
    By fish4fun in forum Trouble Shooting
    Replies: 10
    Last Post: 30-04-2010, 06:47 AM
  2. Replies: 4
    Last Post: 14-04-2009, 09:42 PM
  3. Mitsubishi Electric Intermittent fault
    By marc5180 in forum Air Conditioning
    Replies: 28
    Last Post: 15-01-2009, 10:19 PM
  4. Mitsubishi Electric VRF
    By vijay_study in forum Air Conditioning
    Replies: 3
    Last Post: 06-11-2008, 10:03 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •