    Mitsi R2 problem



    Hi. Have a vrf system with 8 cassettes off bs box but one cassette with it's own remote is going berserk. There is no g50 or bms. All other units run fine set to cool 19, the fan runs on this but has no cooling. Test run it works fine. If you set it to cool 19 after approx 5 mins it either swaps itself to heat 30 or cool 30 but still does no duty. Even if you lock the controller ( par 27) into say cool 30 it still changes itself. Faulty indoor PCb?



  2. #2
    Join Date
    May 2010
    Location
    Newcastle
    Posts
    13
    Rep Power
    0

    Re: Mitsi R2 problem

    Meant locked at cool 19 not 30

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsi R2 problem

    You could just make sure that only this one remote controller is controlling this one indoor unit.
    Use the engineers mode at the remote to check configuration of the indoor units & remote controllers.
    You need to confirm correct configuration of indoor units & remote controllers as with 30v d/c Mnet PAR27 remote controllers can be connected to any indoor unit but will still only control the indoor units according to address setting.
    If 2 remote controllers are controlling this indoor unit & the other controller is in another room then the occupant my be changing it if they dont like cool 19.

    If all seems ok then perhaps some electronic fault with indoor circuit board or remote controller.
    You could try delete the remote controller using engineers mode & then assume control of the unit with another remote controller in the system & then see if the unit works without this problem. That would be quick & easy & would indicate if problem with indoor unit or remote controller.

  4. #4
    Join Date
    May 2010
    Location
    Newcastle
    Posts
    13
    Rep Power
    0

    Re: Mitsi R2 problem

    Fitted new main indoor pcb, cleared faults and all is now good. Thanks for your advice...

Similar Threads

  1. problem with a small cooler
    By corvairbob in forum Trouble Shooting
    Replies: 1
    Last Post: 03-03-2010, 05:19 AM
  2. Mitsi Heavy Industries multi unit problem
    By r0ss in forum Air Conditioning
    Replies: 6
    Last Post: 03-02-2010, 07:07 PM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Replies: 6
    Last Post: 11-07-2008, 03:07 PM
  5. Condensation Problem At Door to Freezers
    By mmarch in forum Air Conditioning
    Replies: 5
    Last Post: 17-10-2005, 02:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •