    Carrier VVVT System



    Hi Guys, has anyone experience of one of these systems. I'm trying to sort out the 'whole system' , not just the Carrier side.

    On the Carrier side, we basically have a load of Slave control units and possibly one (or two) Masters (covers two floors). Each slave controls its own air damper box which is fed from a single common duct which can deliver EITHER warm air OR cool air, but not both at the same time.

    As I understand it, the Master polls the slaves to see what their demand is (ie. either Heat or Cool) and this then itself demands (presumably on the majority) either warm air or cool air from the AHU.

    The AHU is controlled on the building TREND system, the duct pressure being maintained via a pressure sensor and VSDs controlling the supply and extract fans.
    The Trend has x4 temperature set points. x2 Heat and x2 Cool.

    What would the typical duct pressure be on such a system?

    Does anyone know what signals the Carrier Master outputs? Is it 0 -10v for heating and a separate 0 -10v for cooling ? Are there any other outputs (eg fan speed)?

    The other open question is what is the minimum recomended deadband for the room controllers? (ie difference between heating and cooling setpoints).

    As this is in a people training enviroment, the small rooms can get 'stuffy' very quickly, so the input of air on a regular basis is relatively important, which if the deadband is too wide, and the damper box remains shut can happen.

    Your help and advice would be much appreciated.

    As I understand, not many of these systems were installed!

    Regards, Adrian.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Carrier VVVT System

    Hi Adrian, I worked on one of those beasties some years back, I wish you well.

    Various documents are available here...
    http://www.commercial.carrier.com/co...ID4396,00.html

    Can't remember enough about the VVT to be able to help further, sorry.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Carrier VVVT System

    Thanks Brian,

    Adrian

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Carrier VVVT System

    hi, electrocoolman , carrier vvt, you should test each area controler to see if one or more motorised duct vaves are working < in round ducts the valve is egg shapped so it seals correctly<
    when this is proven, you could test the return air, is there a fire shutter that has brocken and the spring return has made it shut? best of luck
    they are not the easyest job to work on .

  5. #5
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Carrier VVVT System

    Hi Sedgy,
    Thanks for the advice.
    The main reason for getting 'to the bottom' of this system is due to a major energy saving drive around our site.

    It was the fact that despite the supply and extract fans being VSD driven, they were running full speed all the time!
    We've discovered that some zone controllers were in full demand due to broken / stuck buttons on the covers, so the system could never ever satisfy their demand and full air flow in these zones.

    Since releasing these, the zones have quietened down, but will check each zone in turn.

    Haven't looked for fire dampers on the system but that's a good point.

    Adrian

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Carrier VVVT System

    adrian, this systemis not run of the mill, without the manual, any eng , wood strugle, if it was me < again < I would get carrier in<expencive but essential <I worked on a site with 2 of these systems in manchester < bea< put the onous on the manufactorer on paper, there are times to pass the parcel- this is the time

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. can't get carrier system #340-020 to work auotmatically
    By carl25 in forum Trouble Shooting
    Replies: 2
    Last Post: 22-02-2010, 07:15 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •