We are modifying an existing refrigeration lines to add a temporary parallel evaporator coil loop. The idea is to isolate the coil, pump down the loop, and then remove the setup till it's needed again. once the coil is removed the system will return to normal single loop operation, but the existing connections that fed the temorary loop would still be present with only the two shut off valves from the liquid and suction lines, and possible threaded caps, from venting refrigerant into the environment. My question is, which Shutoff valve offers the best seal, ball valves or diaphram plate valves?
-
19-05-2010, 02:09 AM #2
Re: Which is better Ball valve or Diaphram plate
I would use ball valves as they have less pressure drop for suction line, but as a precaution install a short section of pipe that is welded closed after the valve. It is then easy to cut this pipe and extend if you ever need to re establish the loop.
-
20-05-2010, 09:37 PM #3
Re: Which is better Ball valve or Diaphram plate
Thank-you. A ball valve on the suction line does make sense, given the need to avoid pressure drop. We were hoping to not have to seal off the temporary loop with a brazed cap, but if that is th only sure way to avoid a sytem leak, then that may be the best solution. Thany you for your help.
-
21-05-2010, 02:54 AM #4
Re: Which is better Ball valve or Diaphram plate
A good quality ball valve will not leak, brazing pipes closed is only a precautionary and saftey measure.
-
21-05-2010, 08:35 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
23-05-2010, 11:34 PM #6
Re: Which is better Ball valve or Diaphram plate
We obviosly still need to review our understanding of physics.
PLEASE ENLIGHTEN US !!!!
-
24-05-2010, 12:44 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Which is better Ball valve or Diaphram plate
Does this brings some light?
Last edited by nike123; 24-05-2010 at 12:51 AM.
-
24-05-2010, 02:30 AM #8
Re: Which is better Ball valve or Diaphram plate
Dont believe presumptions that are not based on scientific evidence.
It is impossible to put a ball with a two inch diameter through a hole of one inch.
It may be more accurate to say materials, welds or mechanical seals may deteriorate over time.
The author in his opening statement contradicts himself.
Put a drop of oil on a sheet of glass FOLLOWING YOUR ARGUMENT THE OIL IS LEAKING THROUGH THE GLASS. THIS IS IMPOSSIBLE THE MOLECULAR STRUCTURE OF THE TWO MATERIALS DOES NOT ALLOW IT .
-
24-05-2010, 06:47 AM #9
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Which is better Ball valve or Diaphram plate
Yo didn't got the picture. Glass bottle will leak at cork-glass junction, not thru glass material itself.
Similar Threads
-
Diagnosing valve plate problems
By Dan in forum The Trail of TearsReplies: 36Last Post: 16-10-2009, 10:37 AM -
LEV does not open
By Yuri B. in forum Air ConditioningReplies: 7Last Post: 19-07-2009, 02:37 PM -
Motorized Ball valve versus Globe valve for modulating application
By Sridhar1312 in forum IndustrialReplies: 2Last Post: 06-02-2009, 07:35 PM -
R22 Flooded System - Trawler
By chiefbecker in forum System OptimizationReplies: 18Last Post: 07-02-2008, 11:11 PM -
valve plate failure
By Andy noblet in forum Trouble ShootingReplies: 6Last Post: 04-06-2004, 08:54 PM