Thread: York ycam problem
-
17-05-2010, 07:57 PM #1
York ycam problem
Hi there,
I recently changed a compressor in a heat pump York Ycam 360.
The compressor is a Copeland D8SJ-6000 with R22.
After start up,i notised white foam in oil glass and the needle of the high pressure gauge instable.
Also the muffler is in strong vibration.
What could be the problem??
-
18-05-2010, 02:48 PM #2
Re: York ycam problem
Hi your instable needle could point that u have air in the sys,the foam could be liquid flood back
and a vibrating muffler dosent sound good ,
for a start i would revaccume the unit to low microns at least 500, make sure there are no leaks and then recharge .
then check your pressures and make sure you are not over charged and make sure u dont have liquid flood back,
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
18-05-2010, 04:39 PM #3
Re: York ycam problem
Thanks goshen.I charged the system by weight 41 kilos.
System superheat is 10 celsious.The previous compressor had broken suction valves and damaged pistons.
-
19-05-2010, 07:14 PM #4
Re: York ycam problem
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
28-07-2010, 09:05 PM #5
Re: York ycam problem
Dear All,,,,I have a problem with York YCAM 240 ..."external Interlock " .....can you help me with it ? ......Thanks
Similar Threads
-
YORK YCUM YCAM Controller (maybe Millenium) Instruction (Manual) required
By Jacek in forum Refrigeration BooksReplies: 20Last Post: 15-08-2010, 11:49 AM -
YORK ducted split
By ALONEI in forum Trouble ShootingReplies: 7Last Post: 10-07-2010, 02:18 AM -
Help to solve problem on York chiller
By nassersh in forum Trouble ShootingReplies: 7Last Post: 03-06-2008, 08:38 PM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM