    Thermistor Check



    Hi Everyone,

    What procedure do you guys use for checking thermistors? I recently checked resistance on one which according to the resistance chart, the thermistor checked good. Later, I determined the thermistor was bad when ambient temperature changed around the thermistor.

    What would you all recommend?

    Thanks to all!



  2. #2
    Join Date
    Apr 2008
    Location
    united states
    Age
    60
    Posts
    29
    Rep Power
    0

    Re: Thermistor Check

    There are two types of thermistors:
    • Positive Temperature Coefficient (PTC) types have a resistance that increases with increasing temperature.
    • Negative Temperature Coefficient (NTC) types have a resistance that decreases with increasing temperature.
    For a small thermistor, put an ohmmeter on it and the heat it up with a blow dryer, heat gun, or the tip of a soldering iron - the resistance should change smoothly (up or down depending on whether it is PTC or NTC type). If the resistance changes erratically, or goes to infinity or zero, the device is bad. However, you will need specifications, temperature measuring sensors, etc. to really determine if it is operating correctly.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Thermistor Check

    HI Husky250
    Do you have a reading or display of the thermistor temp? If so then do a callibration test - compare it with a known accurate thermometer over a period of five minutes and allow time for it to settle first. If it is for chilled water then calibrate in water and ice using an accurate thermo as referance. If there is no display of temp for this thirmister then you must find the resistance comparance chart in the manual or get the numbers off the thermistor and search google for them. Whan compareing against another thermo ensure it is the same type to match the response of sensor. If you need more help with details let me know.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Thermistor Check

    Generally the controller fails in my experience

  5. #5
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Thermistor Check

    Quote Originally Posted by scuba View Post
    There are two types of thermistors:
    • Positive Temperature Coefficient (PTC) types have a resistance that increases with increasing temperature.
    • Negative Temperature Coefficient (NTC) types have a resistance that decreases with increasing temperature.
    For a small thermistor, put an ohmmeter on it and the heat it up with a blow dryer, heat gun, or the tip of a soldering iron - the resistance should change smoothly (up or down depending on whether it is PTC or NTC type). If the resistance changes erratically, or goes to infinity or zero, the device is bad. However, you will need specifications, temperature measuring sensors, etc. to really determine if it is operating correctly.
    Thanks to everyone, this is really good information.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Thermistor Check

    HI maggo :
    not necserally we had some ntc sensores that just died,turns out they were water sensitive.
    water got in to pocket which was not filled with silcone grease.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  8. #8
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Thermistor Check

    I find thermistors do go bad.. thermistors are not linear so you cannot assume that a certain difference in resistance for a degree measurement.. meaning it is not .1 ohms for every .1 degree.. they are usually logarithmic so you must use the chart...

    they are constantly heated and cooled.. and semiconductors over a period of time can and do change their properties so this will cause thermistors to become out of calibration....

    if you have a known good part of the same type you can dump both into the same conditions.. amibent air, a glass of water (for ones that are waterproof), etc and see how the 2 resistance values agree...

    often when im working on mini spliuts the whole bank of thermistors for the indoor unit (or outdoor) will plug into one connector on the board.. pull them off the pipes and subject all to same conditions and then compare.. they will differ slightly but all should be close...

    the only time a unit will issue an error code related to a thermistor is if it is open, shorted, or hits an out-of bounds value that the controller is designed to recognize... ie reads 250 degrees F on an A/C unit....

    with the newer units and EEV's these thermistors are the only feedback as to the refrigerant temperatures and flow inside a coil.. in effect the units measure their own superheat and subcooling.. some units now even take humidity measurements of interior and exterior units to make a better decision on what to do based on wet bulb / dry bulb temperatures...

    your best Kit will even have a mode to calibrate thermistors....

    in effect those little guys have a pretty big role in the performance of a system
    -Christopher

  9. #9
    Join Date
    Feb 2009
    Location
    Israel
    Age
    55
    Posts
    6
    Rep Power
    0

    Re: Thermistor Check

    The best way to test sensor is when the sensor connected to the controller
    We need to check with multi meter In VDC mode.
    Put the probe on the sensor connection.
    At room temperature (25degrees) you will receive 2.5VDC If you receive 5VDC this means that there is a disconnect If you receive 0 VDC means that there is a short
    There is controller that working at 3.3V. In this controller when the sensor is disconnect we get 3.3 VDC. at room temperature (25degrees) we get 1.7 VDC.
    Of course, the result varies according to temperature.

    Robert

  10. #10
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Thermistor Check

    Remove the thermistor from the circuit in which it is used. Most ohmmeters have automatic range finders, but if you need to select a range, start with the highest range and then adjust the range downward after making your resistance measurement.

    Connect the ohmmeter probes to the thermistor. If you get a resistance reading, the thermistor has an extremely high probability that it is not defective. Most thermistors that are defective will be open and show infinite resistance.

    Turn on the blow dryer and direct the air flow at the thermistor. The resistance measurement on the ohmmeter display should decrease. A typical thermistor will decrease from about 10,000 ohms to about 1,000 ohms, although these values can vary with the thermistor model.

  11. #11
    Join Date
    Feb 2009
    Location
    Israel
    Age
    55
    Posts
    6
    Rep Power
    0

    Re: Thermistor Check

    For example.
    Note:
    that the sensor is the same but ZC207 works at 3.3V and 138 works on 5 V.
    Attached Files Attached Files

  12. #12
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Thermistor Check

    all thermistors are different.. not all are 10k thermistors.. some of the chinese splits are using 5k thermistors.. some are using a mixture depending on the range they expect it to be in.....

    and as stated above some send out a reference voltage of 3.3 volts and some send out a reference of 5 volts....

    most often if the Micro is an 8051 or an ATMEL of some type they are using standard 5 volt reference voltages....

    the ultimate concept here is that a thermistor is nothing more than a resistor that varies with temperature...

    in fact using digital pots you can progmatically make a controller "think" its getting whatever temperature you want....

    the micro simply looks at the return voltage it gets back and correlates that to a temperature... some as simple as a lookup table in the controller (for micros that dont have good math capabilities) and some actually calculate the typically logarithmic formula for resistance to temperature conversion....
    -Christopher

    -Christopher