The below diagram is from a 1973 J&E Hall Info / defect Bulletin.
Stating that in order to eliminate the possibility of introducing water into the compressor.
Because as the pressure inside the crankcase of the compressor falls to ambient. The rate of absorption reduces the pressure in the crankcase very rapidly
and water will enter the crankcase. (Yep been there!)
The preferred solution is outlined below:-
Explanation:-
The gas should be vented into an enclosed vessel with a further outlet into a water container.
The amount of water in the container would be less than that required to fill the enclosed vessel. This would then make it impossible for water to enter the crankcase.
I have seen this type of arrangement recommended before but as yet don't know of anyone that applies it.
Does anyone actually use anything like this out in the field?
Grizzly
PS hopefully the diagram is not to small for anyone to see? If it is left click on it and you will be redirected to a larger image!
Just trying a newly recommended way of attachment.Last edited by Grizzly; 30-04-2010 at 11:37 PM.
Similar Threads
-
contaminants in ammonia systems
By Johnny Rod in forum RefrigerantsReplies: 29Last Post: 17-10-2011, 05:26 PM -
Want to be trained as an ammonia operator
By Randy Williams in forum NH3Replies: 7Last Post: 26-11-2008, 08:15 PM -
Releasing ammonia into the environment.
By Tycho in forum NH3Replies: 21Last Post: 03-02-2008, 05:10 PM -
Ammonia and CO2 reactor
By gwapa in forum NH3Replies: 18Last Post: 07-01-2007, 04:50 PM -
New Ammonia Certification in United States
By JerrydNH3 in forum NH3Replies: 11Last Post: 15-08-2006, 03:10 PM