Carrier 5H 40
Ok first post here. Problem is high suction and low discharge.
Carrier 5H 40 is hooked in to a North Star model 40 ice maker. System runs usally high side 150-165 and low side 22. Been running fine, just did the hourly check, H/P 100 L/P 40 and not making ice. Pumped it down to shut off,when it got to the numbers it runs at turned liquid back on and low side went back to 40 in the blink of a eye.
Thanks Burnie
-
24-03-2010, 11:01 PM #2
Re: Carrier 5H 40
Will it actually pump down and hold the standing pressures?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
24-03-2010, 11:06 PM #3
Re: Carrier 5H 40
Yes. I think I got it figured out. Might be a pluged oil line or oil pump is going out.
-
24-03-2010, 11:29 PM #4
Re: Carrier 5H 40
OK, I'm sure you've already got 'em but manuals and documents on the 5H here...
http://www.carlylecompressor.com/cor...TI1251,00.htmlBrian - Newton Abbot, Devon, UK
Retired March 2015
-
25-03-2010, 05:14 AM #5
-
25-03-2010, 10:03 AM #6
Re: Carrier 5H 40
I agree with moideen; need more input. What was the oil pressure?
-
25-03-2010, 11:45 PM #7
Re: Carrier 5H 40
Oil pressure runs around 55-60lbs. The pressure droped to 34 which unloaded the machine. Cleaned out all the oil lines and checked guage.
Fired up compressor and watched oil pressure, went from 53lbs to 30 lbs after about 30 seconds then started going lower. Got down to about 20 lbs. Looks like the oil pump is going out.
-
26-03-2010, 12:14 PM #8
Re: Carrier 5H 40
i want carrier cassete tye unit fault code
-
26-03-2010, 01:10 PM #9
-
27-03-2010, 01:03 AM #10
Re: Carrier 5H 40
There's several things that could be wrong. There is a screen "filter" in the end bell that the control oil goes through (could be stopped up); there's a relief valve located on the shaft end of the compressor that could be cracked or stuck; internal problems with the oil tubing to the unloader mechanisms; hopefully there is an oil pressure cut out in the control circuit or you might as well get ready to replace the compressor.
-
27-03-2010, 06:47 AM #11
-
30-04-2010, 08:05 PM #12
Re: Carrier 5H 40
Sorry did not get back on this. Got slamed with halibut and black cod.
Got it fixed....
the Hydraulic Relay was jambed,had to replace pump end cover to fix it.
thanks for the help,..
Burnie
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Carrier Chillers
By Ed Burris in forum Technical DiscussionsReplies: 6Last Post: 27-03-2010, 02:00 AM -
Carrier 42XPF100 spares availability
By rob_h1978 in forum Air ConditioningReplies: 0Last Post: 11-02-2010, 11:08 AM -
Geoff in NY ~ Carrier Parts
By Futsal1st in forum Trouble ShootingReplies: 6Last Post: 30-12-2009, 04:07 AM -
Help identifying carrier HiWall dom. split
By paul_h in forum Air ConditioningReplies: 4Last Post: 12-12-2008, 09:12 AM