    Remote controller set temp
    System: Daikin VRV III
    Cordet remote controller -BRC1C62.
    Ceiling mounted indoor unit is working but the remote controller not shows the set temp (swing ,mode & fan speed display available on display)
    Your Help on this matter is appreciated
    5,667
    Re: Remote controller set temp
    The set temperature does not show if you select 'Fan Only' mode or 'Dehumidifying' mode.
    Can you see a snow flake or sun symbol at the top of the controller?
    Mar 2010
    India
    100
    Hello Frank, Indoor unit not in use from previous 12 month.For one 28 hp system there is 13 indoor, out of that one is not in use due to some reason. I found water leakage from unit & wired remote controller not shows the set temp. when I start unit from remote controller, found unit is working & it shows the Swing ,cooling & fan speed symbol. I checked field setting found all the second code numbers are factory set.checked proper connection, any loose contact.
    No other mulfunction error code found on remote controller except "A3".
    Is this possibility 1) Expansion valve is in open condition.since unit is not in use so water drop created on coil fins.automatic drain system also not working. 2) there is problem in PCB card.
    (Before one month Daikin service enginner connect the
    Service checker Instrument to this Unit for diagnosis of another indoor unit problem.Is this problem created due to Daikin service engineer mistake ? because before connecting service checker instrument to this unit we have never seen water leakage & set temp issue in the period of 11 month.At Present we are not taking support from Daikin, warrenty period is over)
    5,667
    If there were any faults, the system would be showing an error code. No faults, steady red operation light - no problem.
    The only other time where a wired remote controller does not show a temperature display is when it is connected to a VAM unit only.
    What is the model number of your indoor unit?
    Mar 2010
    India
    100
    Indoor unit Model no -FXFQ100PVE
    Outdoor Model -RXYQ18PY16 & RXYQ10PY16
    Wired Remote controller -BRC1C62
    5,667
    Is the remote controller connected to the P1 P2 terminals as a single controller?
    Mar 2010
    India
    100
    Yes,remote controller connected to the P1 P2 terminals.
    5,667
    Have you tried swapping the controller with a different one on the system?
    Mar 2010
    India
    100
    I swapped the controller with a different one but found no change in existing problem.
    Mar 2010
    India
    100
    Hello Frank, Thanks for your cooperation, Today I interchange existing problem unit PCB card with another unit PCB for troubleshooting.When I connect the another PCB card, remote controller shows the set temp & drain pump also work. & again reconnect the previous PCB card found existing problem so conclude PCB card is faulty. Is this correct ? can we solve problem with help of service checker because strange thing is there in no error code on remote controller.
    5,667
    That was going to be my next suggestion....the indoor fan coil pcb is faulty..looks like you beat me to it.
  1. Relocation Of Daikin Remote controller
    By moondawn in forum Air Conditioning
    Last Post: 11-12-2009, 09:32 PM
  2. Failing remote controller (daikin BRC1D527)
    By ColocMadrid in forum Air Conditioning
    Last Post: 22-06-2009, 08:51 PM
  3. DAIKIN VRV Remote controller
    By 2007eng in forum Air Conditioning
    Last Post: 19-07-2008, 07:04 PM
  4. Compressor loading, cooling, and range of operation.
  5. Stiebel Remote Controller?
    By Makeit go Right in forum Air Conditioning
    Last Post: 24-05-2006, 12:33 AM