Thread: R410A leakage
    Mar 2010
    India
    100
    R410A leakage
    System -Daikin VRV III,Outdoor model -RXYQ18PY,Indoor model -FXFQ100PVE
    What is the easy way to check the R410 leakage ? Is there is any error code for decrease in pressure? then how to find it.
    Nov 2007
    Scotland
    49
    Re: R410A leakage
    Weigh out the charge and compare it to initial charge there is no quick fix!
    Jun 2009
    North East England
    712
    Re: R410A leakage
    Providing that the system comissioning was done correctly i.e autocharge function,full learning curve were carried out the VRVIII can perform a refrigerant containment check then using the binary codes you can work out the amount lost but if the system does have a leak on it you need to carry out recovery setting and pull the gas and pressure test.
    follow this link
    www.extranet.daikin.co.uk
    for the service manuals for this kit it'll tell you how to carry out the above functions
    Si34-601 should be the manual you require
    edit: use http://extranet.daikin.co.uk , but you will need to register on the site.
    Dec 2008
    563
    Re: R410A leakage
    You may be able to get some indication from the service code 41, which wil give an indication of the air and coil temperatures. If the system is short of refrigerant there should be a noticeable difference in values when compared to the expected or previously observed. However if the system is only slightly short, the temperature may still be acceptable. Only sure way is to reclaim and weigh the refrigerant as previously suggested.
  1. Pipes to large for R410a??
    By Spanglishsparky in forum Technical Speculations
    Last Post: 09-05-2009, 12:57 AM
  2. My freezer inner pipe leakage
    By syaful in forum Domestic
    Last Post: 05-03-2009, 10:52 AM
  3. Pressure Testing for R410a
    By Pooh in forum Tools and Calculators
    Last Post: 13-08-2008, 11:41 PM
  4. R410A pressure in air conditioning
    By irwinchong80 in forum Technical Discussions
    Last Post: 06-10-2007, 07:33 PM
  5. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    Last Post: 27-11-2003, 09:05 AM