Results 1 to 16 of 16
    Dec 2008
    manchester
    5
    heres one for you
    cold store, -22, r404a.
    little comercial / light industrial job.
    has a suction seporator on the system....
    ...heres my problem.
    bringing liquid back to the compressor, now i have checked the fan coils are clear, fans running fine, checked expansion valve super heats, both ok (about 6 degrees) liquid line SV wroking correctly, the system is not over charged either.
    i really do think ive checked everything i can.
    any other suggestions???
    Apr 2001
    79
    5,071
    35
    Re: heres one for you
    If the superheats at the evap outlets are 6K, then it can't have liquid entering the compressor.
    Split Croatia
    6,151
    Quote Originally Posted by murphyboy View Post
    Check suction superheat at compressor suction and measure pipe temperature 25 cm from compressor.
    Use precise and calibrated gauges and thermometer. Zero your gauges for altitude. Isolate temperature probe and pipe at measuring point. Use appropriate probe for job. Wait 2 min or more before temperature reading. Post new readings including:
    Evap air in temp
    Evap air out temp
    Saturated suction temp (convert from pressure)
    Suction line temp at evap outlet
    Suction line temp at compressor inlet
    Cond air in
    Cond air out
    Saturated condensing temp (convert from pressure)
    Liquid line temp at condenser outlet
    Explain do you have any suction/liquid line heat exchangers and at what points you are measuring pressures and how far from temperature measuring points.
    Aug 2008
    55
    259
    Got a liquid line/Suction line heat exchanger anywhere in the system perchance?
    May 2009
    Sydney
    73
    May be leaking liquid / suction heat exchanger inside fan coil unit.
    Apr 2001
    79
    5,071
    35
    Until we see the compressor inlet superheat, we have no evidence that there is a floodback problem.
    Dec 2008
    manchester
    5
    ive taken my pressure from a schrader point i brazed onto the exp equalising line. if i was leaking liquid id expect to be seeing stupid pressures at my suction wouldnt i?
    there is a small slop pot which the liquid line does pass through, but as before if liquid at discharge pressure was leaking into my suction id have daft pressures.
    3,853
    What makes you think the system may have liquid returning to the compressor?
    38
    The TX vav is obviously hunting, satuarting suction, equals flood back.
    Dec 2008
    manchester
    5
    ice build up around the compressor windings (bitzer sealed comp), ice cold on suction side of cylinder head, oil sep with frost, oil flushed from compressor sump.
    txv is working fine
    Split Croatia
    6,151
    That doesnt mean liquid in compressor. That only mean that suction line temperature and part of compressor is below 0°C. If room is -22°C than evaporation temp is around -27°C to -30°C.
    You must have than 27K suction superheat to get rid of ice at suction.
    Same as above!
    That is probably related!
    txv is working fine
    Maybe, but 6K superheat at design temperature is litlle to high.
    Why is that hard to take measurements we asked, and post it here, than we could make our own conclusions?
    Mar 2009
    KZN, South Africa
    64
    2,212
    Good points, Nike.
    Aug 2009
    New Zealand
    2,554
    I am in the manchester area (today), If you need a second pair of eyes, I can assist, cost you a cub of cha and a bacon butty. PM me if you need help
    ekeller's Avatar
    ekeller Guest
    if ice on seperater may mean you have very cold vapor at-22degress doesnot mean u have liquid
    Feb 2010
    242
    As others have said.
    Frost on the suction can garentee one thing only.
    The suction is colder than 0 deg C.
    Cool runnings.
    38
    The enthalpy of vapour will not form ice on suction, unless satuarated, the degree of saturation is the key.
    So what is the SST at compressor, and what is the superheat?