05-02-2010, 07:21 AM #151
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thank you for your comments, Transcold...One problem I have is I can't find a compressor to my reefer with model no. 06DR241BCC06C0
-
26-02-2010, 07:59 PM #152
-
26-02-2010, 10:32 PM #153
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic, I have Thermoking C11/M40 been off for four days. On switch on unit shows fault code 10 high refrigerant press/temp, ambient here at present 3 degrees C unit also faults 38 lithium batt. any ideas?
-
28-02-2010, 07:10 AM #154
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
...................
Last edited by reefermechanic; 27-02-2013 at 09:02 AM.
-
28-02-2010, 08:13 AM #155
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi all,
i attached 2010 Marine Solutions Americas Training Brochure to the here..
Also carrirer training program;
https://www2.carrier.transicold.com/...adedb?OpenView
have a nice day.
reefer mechanic.
-
28-02-2010, 08:29 AM #156
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi all,
for daikin......
contact adresses..
Europe Office
daikineu@xs4all.nl
North America Office
reefteck12@cs.com
South East Asia Office
goh.choonleng@grp.daikin.co.jp
South America Office
alvaro.quintana@adinet.com.uy
robert.ferreyra@adinet.com.uy
-
28-02-2010, 04:18 PM #157
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Reefermechanic, as stated a reefer in Uk is for refrig container shipment. No engine. I have a CF11/M40 on a customers sight it has been off a week and ambient here at moment 3 degrees C standing press 6.75 bar R134a when switched on alarm code 10, & 38 will be displayed motor does not energise at all have tried dissconecting dischrge sensors still will not run. any advice would be apreciated
-
08-03-2010, 10:39 PM #158
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Does anyone have the User manual for Thermo King SmartSponge Software.pdf ?
can you forward to mfz@primetronics,biz
many thanks
-
12-03-2010, 12:25 PM #159
Latest Software for Daikin reefer
Hi does anyone has latest Daikin Reefer software. I am having V6.04. Appreciate if someone could mail to me at ekbal@shmaritime.com
Thank You.
-
12-03-2010, 08:32 PM #160
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermech sorry for delay in responding, thanks for your help. I have unit up and opperational. I went through all control switches and contactors systematicaly till i traced fault. When I had no early answers from thread went to old fault finding method. scratch head and test every thing. Thanks again for your efforts hope I can return the favour
-
18-03-2010, 06:54 AM #161
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear all
i work in small container terminal in Hong kong,How can i get information about the reefer container alarm ?
thks
-
19-03-2010, 03:06 AM #162
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear Bro,
Could you please tell me about carrier reefer (69NT40-541 301)? This unit was showing datacorder alarrm (dal 71).Please advise what should I do it?
-
21-03-2010, 06:35 AM #163
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear Mech,
Hope you well. I have a carrier utra that keeps cutting out on low battery. Have placed new battery but still same problem. Is there any way I can stop the the unit from switching off until I have offloaded and get it back to my yard.
Hope you can help
Cheers
Leon
-
21-03-2010, 07:59 AM #164
-
22-03-2010, 02:56 PM #165
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Gents.
can some one assist to find the Reefer Data cable connector. for daikin/carrier/thermoking and Starcool.
i need to buy them ....
-
26-03-2010, 09:02 AM #166
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Any QCM/IRS techs on here??
-
26-03-2010, 10:46 AM #167
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi!! every one i am new reefer mechanic but i was HVACR mechanic i am new here so i hope someone can help me in the next other day.
thanks.
-
26-03-2010, 10:52 AM #168
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
i think you can try change into R404a i do it already that then its working good
-
01-04-2010, 06:27 PM #169
-
01-04-2010, 06:46 PM #170
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
06-04-2010, 03:32 AM #171
-
09-04-2010, 03:43 AM #172
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I'm working on a reefer container it's compressor over heating due to no refrigerant in the system, but i don't see any leaks on it what could be the problem.
-
16-04-2010, 07:32 AM #173
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi ethis is moorthy from qatar, anyone can send me that download link for thermoking reefer manual.
TRY TO LEARN MORE ABOUT A/C SYSTEM
-
16-04-2010, 07:46 AM #174
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
check your condencer and condencer fan motor running speed, check power line of compressor.
TRY TO LEARN MORE ABOUT A/C SYSTEM
-
19-04-2010, 10:04 AM #175
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
DEAR SIR,
THANK U, SIR. FOR YOUR REPLY.
I have one problem for the THERMO KING unit.CRR-40
rgs the temp pulldown very slow comp suc pruss vacumm, discharge pruss 60psi. set pt-18 ret temp+2c, sup-7c .before starting suctpruss 60psi,kvq value teMP-40C.
Kindly advise sir,
jnb.
-
22-04-2010, 04:26 AM #176
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear sir,
pls rply.
-
22-04-2010, 04:28 AM #177
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
dear sir,
pls reply.
-
22-04-2010, 01:27 PM #178
-
22-04-2010, 07:53 PM #179
-
22-04-2010, 07:56 PM #180
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Dhirendra
I think you need old reefer unit. You have to contact to SmithHolland.
http://www.smith-holland.com/reeferservice.htm
best regards.
Reefer mechanic
-
22-04-2010, 07:57 PM #181
-
22-04-2010, 08:06 PM #182
-
24-04-2010, 06:16 AM #183
-
26-04-2010, 08:05 AM #184
-
08-05-2010, 01:53 PM #185
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Have sombody experiance whit a diesel/elektical reefer
45ft slx 300 from themo king
thanks
-
11-05-2010, 01:40 AM #186
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
help with thermo king cbci unit compresser is pumping ***** but nothing geting cool in air handler
-
13-05-2010, 02:53 PM #187
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I need alarm list for mitsubishi cpe 14 .Thanks .nickzarin@gmail.comLast edited by nickzarin; 13-05-2010 at 02:58 PM. Reason: mail address
-
15-05-2010, 02:29 AM #188
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Will this do ?
http://mhiks.mhi.co.jp:13081/acrmw/s...E14-2BA3ES.pdf
-
15-05-2010, 03:53 PM #189
-
16-05-2010, 07:14 PM #190
-
18-05-2010, 06:39 AM #191
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please help me reefermechanic.
how to reset reefer alarm (carrier transicold) if the display is written AL52?
-
18-05-2010, 05:27 PM #192
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi James, all of Carriers container manuals are available on their website.
Carrier Container Manuals
AL52 = "Alarm list full",,,,,scroll through the alarm list and see what the other alarms are and post back.
-
19-05-2010, 03:35 AM #193
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thx a lot...Will
-
24-05-2010, 11:24 AM #194
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please help me.
I need Thermoking ThermoGuard MPIV User manual
-
24-05-2010, 11:54 AM #195
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
30-05-2010, 08:19 PM #196
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
People, help me please-e-e-e. I have a problem with controller MP-3000. A LCD display show EMERGENCY PROGRAMM what is that? When i want to enter to MAIN MENU and press the keys F2 and F3 nothing happens .Sorry for my bad english i hope you are understand me.
-
13-06-2010, 07:19 PM #197
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
v500 2008. not running on electric. unit does self check then then the screen goes blank 12v truck. good 3 phase good 12v from transformer. changed micro p, transformer, cab controller no good. any idea. Dealer called not fixed yet!!!
-
22-06-2010, 05:52 AM #198
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
What is it what you want to keep "cool" when the ambient temp is -40?
-
22-06-2010, 05:54 AM #199
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
No,only fill the right *****, r404a runs with much higher pressures.
-
25-06-2010, 05:30 PM #200
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM