Time delay for multi compressors
Hi,
Need another opinion.
I'm in the process of installing some large split a/c systems to a building. Four of the systems are linked to one controller (looped together-one master and three slaves) These are 16 kW each. When the controller is activated, all the compressors are going to start at the same time, which I don't want to do, because each time they start up, the lights will dim.
I had thought about making a control system, mounted on a DIN rail linked into each of the compressors to give a time delay on the load side of the contactors, but noticed that there are some manufacturers-Eberle and Aspen who make time delay controls at a decent price.
I can't decide what to do. They are 3 phase systems 415VAC, so can anyone recommend a product to do the job for me please.
Regards
James
a problem shared is a problem halved
-
05-11-2004, 11:20 PM #2
Re: Time delay for multi compressors
Depending on the manufacturer some have a built-in time delay to provide load shedding on start up; check with them first.
You idea of a time delay on the load side of the contactor ?? Do you mean to interupt the 3 phases ?
Surely it would make more sense to to put them in the contactor coil circuit.....
You could fit ON DELAY timers to each contactor with different times on each one ?
Your move....Brian - Newton Abbot, Devon, UK
Retired March 2015
-
05-11-2004, 11:41 PM #3
Re: Time delay for multi compressors
Hi Brian,
I don't think there is a facility built in, and yes it would probably make more sense to place on the contactor coil-that was my other option once I have the coil voltage and amps etc.a problem shared is a problem halved
-
06-11-2004, 12:03 AM #4
Re: Time delay for multi compressors
Try this: http://www.icmcontrols.com/ This seems to be a simple solution to tie into control contactor
ICM 105 | Ideal For Compressor Staging
Low holding current
Low cost version of the ICM102 without the cooling anticipator circuitry
Ideal for compressor staging
Universal voltage operation
Knob-adjustable time delays
Simple 2-wire hookup & up to 10 min adj timing
-
06-11-2004, 12:13 AM #5
Re: Time delay for multi compressors
Hi Guys,
Subject "Time delay on multiple compressors"
Anyone else come accross these stupid Norpe integral daries that use a light tube starter as a time delay to bring on the second compressor. I know these units are made cheap so they sell more by surely they can come up with something better than that
Regards
Raymond
-
06-11-2004, 08:05 AM #6
Re: Time delay for multi compressors
Hi Iceman,
Looks like you've been busy.
A serial timer is the ultimate solution, simple and cheap.
I usually use the Supco TD 69, you can get it everywhere in the UK.
You only need a few seconds TD between the compressors.
Good luck.
Chemi
Similar Threads
-
Delay on Timers
By Feeze in forum ElectricalReplies: 27Last Post: 14-10-2009, 09:20 PM -
Pull-down time for residential unit
By TooLittleTimeZZ in forum DomesticReplies: 25Last Post: 18-03-2006, 01:27 PM -
Compressor's volume efficiency
By John McGru in forum FundamentalsReplies: 0Last Post: 16-02-2004, 08:44 AM -
Remanufactured compressors
By Peter_1 in forum Industrial CompressorsReplies: 1Last Post: 13-01-2004, 04:16 PM -
Fridge compressor's can anyone explain why this happens....>
By electro in forum DomesticReplies: 10Last Post: 24-07-2002, 02:30 PM