    Daikin high pressure switch. E3 fault



    Hi guys I have been having problems with a condenser vrv. It's out on high pressure switch e3 fault. Checked for abnormal power and is all fine. But it's cuts out on e3 wohout eve trying to run. Tried turning off an on again and fault comes straight back so I can't even run it to see if it is running at to higher pressure. Any ideas where to start? Should I do a restart and put it back threw a test run?

    Many thanks guys



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    563
    Rep Power
    24

    Re: Daikin high pressure switch. E3 fault

    It could be a faulty HP switch or possibly a fault on the relevant section of the PCB. Check the wiring to the pressure switch and check for continuity etc. You may need to reset the system at the outdoor PCB as the fault code will be stored. Which model is the VRV?
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Daikin high pressure switch. E3 fault

    High pressure switches on VRV systems are 240v normally closed under normal conditions. This is the first thing to check. If the system is VRV III, then a nanual rest is required. To do this, simply stop the operation of all indoor units by remote/centralised controller, then press the return button once on the outdoor unit main pcb. LED H2P on the bank of seven will then go out and the system will be locked out for a period of around 10 seconds, then the system will be able to be re-started. This was added to the software of VRV III systems. Powering off the outdoor unit will also reset the problem, but only if all indoor units are stooped. Hope this helps, let me know how you get on

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. daikin, high pressure??
    By airconadam in forum Air Conditioning
    Replies: 8
    Last Post: 11-10-2007, 10:09 PM
  4. high pressure protection
    By karimihassan in forum Air Conditioning
    Replies: 11
    Last Post: 18-08-2007, 06:52 PM
  5. Oil Pressure Switch
    By Abe in forum Commercial
    Replies: 9
    Last Post: 15-03-2003, 11:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •