    Over condensing?



    I have heard the expression "over condensing" but have never come accross a problem that has been caused by it so i don't actually know what the effects of it are?

    Can anyone shed any light on this for me please?

    I'm thinking that if the refrigerant is over condensed then the head pressure is dropped thus causing low suction pressure?

    Fan speed controllers are used to maintain a certain head pressure and therefor eliminate over condensing, but why are they only installed on certain refrigeration equipment?

    I would be very grateful if someone could help me with this.

    Thanks, Sam



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Over condensing?

    Quote Originally Posted by samisonfire View Post
    I have heard the expression "over condensing" but have never come accross a problem that has been caused by it so i don't actually know what the effects of it are?

    Can anyone shed any light on this for me please?

    I'm thinking that if the refrigerant is over condensed then the head pressure is dropped thus causing low suction pressure?

    Fan speed controllers are used to maintain a certain head pressure and therefor eliminate over condensing, but why are they only installed on certain refrigeration equipment?

    I would be very grateful if someone could help me with this.

    Thanks, Sam
    Hi Sam.

    You are right in what you assume re head pressure
    but the big problems comes if the head preasure drops too low then the TEV's don't work correctly and the whole system falls over.

    Think of a condenser on a roof in the depth of winter and with wind chill the condensing temp just fall through the floor which then cause's the liquid to log in the condenser. That results in the suction pressure dropping also.

    Cheers taz

    .

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47

    Re: Over condensing?

    Well said Taz.
    Hi Samisonfire.
    I think I am correct in saying technically you cannot "over condense".
    But you can loose control of the liquid line temp, resulting in insufficient "Lift" ( Pressure Temperature diff between the LP and HP sides of a system).
    A particular problem on start-up for some systems.
    So when you have lost control of your "Head Cooling" you could say your system is over condensing.
    Grizzly
    Grizzly

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Over condensing?

    Hi there,

    As mentioned by the experts :
    THERE IS NO OVER CONDENSING!!!!!!????

    If ambient temperature drops OR a huge (Surface area = Infinity) condenser is used, the condensing temperature corresponds to ambient temperature and condenser Delta T.
    When consenting temperature drops below design then TEV starves the evaporator and suction pressure falls.

    Head pressure control keeps the condensing temperature near the design value.

    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Over condensing?

    Some very interesting comments. Thank you taz, grizzly & lana.

    I learned something today.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Over condensing?

    without getting to complex, what is intersting, if you drop your SCT by 5C and SST by 5C, your COP soes not change much. So if you do not care about RH or freezing of the evap, then let the system reach equalibrium (as long as in range of the comp) Practically your SCT would drop but your SST would not drop as much, thus actually increasing the COP.
    A bit of food for thought

  7. #7
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: Over condensing?

    Quote Originally Posted by mad fridgie View Post
    without getting to complex, what is intersting, if you drop your SCT by 5C and SST by 5C, your COP soes not change much. So if you do not care about RH or freezing of the evap, then let the system reach equalibrium (as long as in range of the comp) Practically your SCT would drop but your SST would not drop as much, thus actually increasing the COP.
    A bit of food for thought
    never seen so many abbreviations used in a thread ever pmsl

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Over condensing?

    Balanced port TXV's were developed for this very problem. They require less dP to function properly, thus the head pressure can be lowered.
    Last edited by Gary; 20-04-2010 at 05:59 PM.

  9. #9
    Join Date
    Apr 2010
    Location
    oxfordshire
    Age
    40
    Posts
    15
    Rep Power
    0

    Re: Over condensing?

    Thanks for your help everyone.

    When you guys have said about insufficient lift and starving the TEV does this mean that the head pressure has dropped so much that there isn't enough pressure to push the refrigerant through the valve?

    What the symptoms be for "over condensing"?

    Low suction pressure
    Low discharge pressure

  10. #10
    Join Date
    Apr 2010
    Location
    oxfordshire
    Age
    40
    Posts
    15
    Rep Power
    0

    Re: Over condensing?

    Sorry, i pushed the wrong key!!!!

    What would be the symptoms for "over condensing"?

    Low suction pressure
    Low discharge pressure
    High superheat?
    High subcooling?

    If i came across a system that had low suction pressure, low discharge pressure and it was in low ambient conditions i would try restricting the air flow across the condensor to see if that improved the performance of the system before carrying out a leak test, but i am trying to learn the techniques of using subcooling and superheat to fault find so i think this is probably a time where those techniques would come in useful.

    Thanks, Sam

  11. #11
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Over condensing?

    Someone said to me that a-20c freezer room with a TEV + receiver was over condensing and that is what is causing the suction line to freeze..

    Anyone care to comment on this remark?

  12. #12
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Over condensing?

    Quote Originally Posted by multisync View Post
    Someone said to me that a-20c freezer room with a TEV + receiver was over condensing and that is what is causing the suction line to freeze..

    Anyone care to comment on this remark?

    I think that the suction being below 0 is more than
    likely to cause it to freeze, but what do I know

    Cheers taz

    .

  13. #13
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Over condensing?

    Quote Originally Posted by samisonfire View Post
    Thanks for your help everyone.

    When you guys have said about insufficient lift and starving the TEV does this mean that the head pressure has dropped so much that there isn't enough pressure to push the refrigerant through the valve?

    What the symptoms be for "over condensing"?

    Low suction pressure
    Low discharge pressure
    Yes.

    Manufacturers may have different figures but I was
    always led to belive that you need a minimum
    of about 7 bar accross you valve for it to opperate
    correctly.

    taz.

    .

Similar Threads

  1. Remote fitted condensing unit
    By Rayin in forum Fundamentals
    Replies: 6
    Last Post: 14-04-2010, 07:25 PM
  2. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  3. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  4. condensing unit selection?
    By ibraheem in forum Technical Speculations
    Replies: 0
    Last Post: 28-05-2008, 06:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •