20-04-2010, 11:51 PM #1
R12 replacement
Hi guys
I have a CRC reach in cooler The system has a leak. I want to change out the compressor.(Afraid it sucked in contaminents) What would you change the system to. Temp Im looking for is 36 to 40 degrees F. What should I flush the system with. Thank you ahead of time
-
21-04-2010, 09:03 AM #2
Re: R12 replacement
R134a may be suitable, it should run on similar pressure to R12. There is a limited choice for flushing, especially if this is a capillary system. It may be best to purge with OFN to get any remaining contaminents out. Once you have purged a couple of times, then fit the new compressor, fit a liquid line drier and leak test, then give the system a good vaccing out and charge with R134a using the manufacturers charge weight as a guide. Run the unit on test and trim the gas charge if necessary.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
-
21-04-2010, 10:47 AM #3
Re: R12 replacement
I would use a drop in replacement for R12 instead of R134a, such as R49/R413A as it will work better with any residual mineral oil that is in the system from the old compressor. Charge weight is typicaly 80/90% that of the original R12 charge but you will need to watch it run down to set temp a few time to adjust the charge for best operation.
As Hyperion says, a good vac and a new drier, i might be tempeted to put one in the suction too if there is a lot of contaminants in the system.
Let us know how it goes
-
22-04-2010, 12:20 AM #4
Re: R12 replacement
I may put in hot shot does that take 80-90 pct charge also?
Thank you
-
22-04-2010, 04:08 AM #5
Re: R12 replacement
Yes sir Randy. I actually just charged an old R-12 system with Hot Shot today. The charging chart says tha you need 80% of a standard charge with R-414b (Hot Shot). The system is moving heat wonderfully and I'm pretty pleased.
-
22-04-2010, 04:44 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: R12 replacement
DuPont refrigerant _Replacement_Guide.pdf
http://www.mediafire.com/?z2ymtfykw2y
Similar Threads
-
R22 replacement
By brad__34 in forum RefrigerantsReplies: 28Last Post: 04-06-2010, 09:06 PM -
Replacement for R403b
By fridgability in forum RefrigerantsReplies: 2Last Post: 20-08-2009, 03:36 PM -
Replacement Chiller Barrel Selection
By archibaldtuttle in forum Air ConditioningReplies: 0Last Post: 09-06-2009, 08:09 PM -
Replacement Screw Compressors
By dkemper in forum Technical DiscussionsReplies: 2Last Post: 13-10-2007, 07:22 PM -
F 11 replacement for flushing
By andrewuk in forum RefrigerantsReplies: 1Last Post: 17-10-2003, 11:03 PM