    60A Circuit Breaker/MCB



    Is a 60A MCB enough given the spec of the equipment below:

    Type: VRF
    Capacity/HP: 32 HP
    Running Current: 49.5A (3 phase)
    Built in Starter: Yes

    Your help on the above matter is greatly appreciated. Thank you.



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 60A Circuit Breaker/MCB

    Hi your running current as stated is 49.5 amp!a 60 amp mcb should be able to handle this load ,but u should check starting charecaristics of mcb so it could handle starting current.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: 60A Circuit Breaker/MCB

    The rating of the MCB is to protect the electric cable.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2009
    Location
    Malaysia
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: 60A Circuit Breaker/MCB

    If our equipment is a soft starter type (amp started gradually until it reaches full load), should be no problem right?

  5. #5
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: 60A Circuit Breaker/MCB

    You appear to be working back to front, as Frank indicated, the CB is just there to protect the cable.

    You should decide on the cable, to maintain voltage drop and current rating within specifications, and then decide on the Circuit Breaker.
    Last edited by stefs_cruiser; 16-04-2010 at 07:53 AM.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: 60A Circuit Breaker/MCB

    Quote Originally Posted by stefs_cruiser View Post
    You appear to be working back to front, as Frank indicated, the CB is just there to protect the cable.
    I think you meant BRIAN

  7. #7
    Join Date
    Jan 2010
    Location
    wales
    Age
    56
    Posts
    55
    Rep Power
    15

    Re: 60A Circuit Breaker/MCB

    a mcb is a overload protection device it is there to protect all items that are connect to it ie cable and machine if the running current is 49.5 amps with soft start then you should have no problem but if your start up current exceeds your mcb rating then this would cause the mcb to trip same goes for protecting your machine if for instance your compressor stuck this would increase ampage therefore trip before any other damage is caused this is why you should always select the right mcb for the equipment being installed

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: 60A Circuit Breaker/MCB

    The motor should be protected by an overload, set 10-20% above FLC.

    The MCB is there to protect the cable.

    The MCB should be rated as close to but higher than the load current, and the cable should be rated higher than the MCB.

    Example:

    Motor FLC 21A
    Overload set at 24A
    MCB (type 3) 32A
    Cable rated 34A
    When selecting a cable size, be sure to apply the de-rating factors to the equation

  9. #9
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: 60A Circuit Breaker/MCB

    The Fault current overloads and short circuits can be detected by circuit breakers like MCB’s MCCB’s & HRC Fuses etc. But, Circuit breakers don’t detect leakage currents, which are dangerous for humans and livestock and if not detected, can lead to fire hazards. We need a solution that detects such leakages currents and disconnects the circuits from the power Supply & The solution in the form of RCCB (Residual Current Circuit Breaker) also
    Known as ELCB (Earth Leakage Circuit Breaker) which provides protection against Fault current overloads and short circuits & direct and indirect contact of personnel or livestock and against probable fires.
    So you need to choose the proper rating of RCCB / RCBO by considering starting current, Required “No of pole”, Rated full load current & tripping time
    For current rating selection, check the equipment rated full load current (Not the running current)

Similar Threads

  1. Samsung AQV-12MSA Electronic circuit
    By Steve G in forum Air Conditioning
    Replies: 1
    Last Post: 13-04-2010, 10:42 AM
  2. Seperate Circuit Required??
    By CLoSeR in forum Air Conditioning
    Replies: 14
    Last Post: 19-03-2009, 09:15 PM
  3. Replies: 27
    Last Post: 05-03-2009, 11:20 AM
  4. indirect heating circuit
    By CCLPaul in forum Tools and Calculators
    Replies: 0
    Last Post: 26-02-2009, 01:03 PM
  5. refrigeration circuit symbols
    By neil sailes in forum Fundamentals
    Replies: 4
    Last Post: 23-06-2004, 08:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •