Thread: Air Cooled Chiller & AHU
-
02-04-2010, 03:53 AM #1
Air Cooled Chiller & AHU
Pls help me regarding this issue..
Will there be any problem if the piping between the air cooled chiller and AHU is very near? The system is a 1 to 1 system...
Thank you...
-
02-04-2010, 08:10 AM #2
Re: Air Cooled Chiller & AHU
This will depend on chiller loading charicteristics (staging) and the control of the load of AHU. Whether it is DX or chilled water. There could be shot cycling at loads lower than 50%. Let us help you more by providing some more details of the particular system.
-
02-04-2010, 11:52 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Air Cooled Chiller & AHU
Do you have chiller with water tank inside chiller body?
-
02-04-2010, 05:11 PM #4
Re: Air Cooled Chiller & AHU
Why not use a Packaged-type aircon unit if its only a 1-1 system?,what is the capacity of your AHU and Chiller?,I presume you have a chilled water system..
-
03-04-2010, 12:00 PM #5
Re: Air Cooled Chiller & AHU
I think u choose DX system for 100% air intake,for the minimum distance between AHU & Chiller or ACCU please see unit catalogue.
-
16-04-2010, 01:39 AM #6
Re: Air Cooled Chiller & AHU
Dear all,
The capacity of the system is 82 RT.
The distance between the air cooled scroll chiller and the AHU is 61m.
Will it be any problem if the piping between the two is too near? For example, pressure increase due to the circulation inside the system too short...
-
16-04-2010, 08:07 PM #7
Re: Air Cooled Chiller & AHU
Providing your flow rates are within the chiller specification, the pump is sized correctly to handle the pipework pressure drop and the pipework is correctly insulated to prevent excessive heat gain into your chilled water circuit - you should not have any problems.
The only drawback is excessive energy use to chill a large water circuit.
Similar Threads
-
McQuay Air Cooled Chiller
By allwyn-kms in forum Air ConditioningReplies: 8Last Post: 06-10-2009, 03:09 PM -
Refrigerant Temperature in the Water/Air Cooled Chiller
By jinx in forum FundamentalsReplies: 16Last Post: 19-02-2009, 11:43 PM -
Trane air cooled chiller burnt out
By Sridhar1312 in forum Air ConditioningReplies: 0Last Post: 06-02-2009, 10:44 AM -
Comparison sheet 10 ton air cooled chiller versus vrf versus conventional split
By abbasi in forum FundamentalsReplies: 6Last Post: 27-11-2008, 09:52 AM -
De superheater in Air Cooled Chiller
By Rabindra in forum Heat PumpsReplies: 5Last Post: 28-11-2007, 12:13 AM