Results 1 to 16 of 16
    Dec 2005
    228
    dirty condenser signal light
    I am looking to install a light to signal when the condenser is dirty so the user could perform maintanence. It would come on before the high pressure cutout trips. I see two possibilities. One being a fan cycle control that makes contact on rise of pressure just below the safety cutout and lites the signal that the unit needs cleaning. Or a temp control with probe strapped to the hot gas line doing the same thing.
    My question is which would be prefered and where would I sample the pressure or temperature to initiate the sequence. Thanks, Ken
    Feb 2008
    adelaide sth.oz
    1,015
    Re: dirty condenser signal light
    why not fit another h/p control or an encapusulated pressure switch with a fixed range
    5,667
    .....or a differential pressure switch over the condenser
    Why not get the user to enter into a maintenance agreement.
    That way they don't have to think about it because you will do the work for them and that is how the money goes around.
    Dec 2005
    228
    This would defiately be the way to go but
    I have tried to find an encapsulated switch that makes on rise that has the right Make and Break psi. it seems they are only made as safteys and break on rise which would then require a relay further complicating things.
    I work for the manufactuer that wants more sizzle on thier steak. Just started using a ranco fan cycler connected to the hot gas line. It works but the differential is wider than desired. I have been thinking or using the carel control that has a third temperature probe which could possibly used to turn on an indicator light
    Am I ok connected to the hot gas before the condenser or would the liquid line be beter? ..Ken
    Apr 2001
    79
    5,071
    35
    I would go with cond dT.
    Dec 2005
    228
    Gary, I had thought of that but just couldn't figure out how to get it done. Suggestions? Ken
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by kengineering View Post
    Do I get a consulting fee?
    Monitor the temps of the air entering and leaving the condenser, subtract entering from leaving, trip the alarm when the difference (dT) exceeds pre-determined value.
    Of course, if the fan speed is controlled the alarm would only be enabled when the fan is running 100%.
    Dec 2005
    228
    I'll look you up next time I go fishing in FL. for that consult fee. Although we're just tring to hold on to our jobs here in NJ. It could be a while.
    Just to clarify. I'm not actually cycling a fan with the Ranco. Set around 400 psi coil gets dirty, head goes up switch makes and lites an indicator. After cleaning the coil the lower head pressure is realised with the differntial set , lite goes out. It works fine and so far reliable but it's clunky.
    I couldn't come up with a simple delta-T system.
    My next attempt will be to get an accurate temp reading on the hot gas line. strap a temp probe with a programed temp and differential too turn the lite on and off. Then I can make a choice from a production standpoint.
    Just trying to think of all possibilities. Thanks , Ken
    Split Croatia
    6,151
    I
    http://www.ojelectronics.com/Differe...mostat-65.aspx
    Apr 2001
    79
    5,071
    35
    That looks like a winner to me, Nike.
    Split Croatia
    6,151
    Or this ESF-35-1 airflow transducer with relay:
    http://www.ojelectronics.com/AIRFLOW...DUCERS-97.aspx
    Feb 2008
    adelaide sth.oz
    1,015
    their are electronic controllers with this function,sensing liquid line temp,in alarm state the display flashes with its fault code.
    oops i see you have already mentioned carel,definitly the easier way out me thinks
    Apr 2010
    295
    ever thought about a three month timer ?
    Split Croatia
    6,151
    Zelio!........
    Apr 2010
    295
    why make it more complex than it has to be sorry if my timer idea offends just seemed simple if condenser blocks regularly put a timer in for optimal time less to go wrong
  1. Superheat and Subcooling
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Last Post: 30-07-2008, 12:21 PM
  4. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Last Post: 02-03-2008, 06:10 PM
  5. How many forum posters does it take to change a light bulb....
    By taz24 in forum Chit Chat & Service Stories
    Last Post: 04-02-2008, 07:05 AM