    Trane chiller problem



    Hi Guys

    We have a pair of Trane RTAA chillers connect to a BMS panel with a Trend controller.
    Whilst i was carrying out maintenance on the pump sets (auto changeover etc) the chillers locked out.
    The chiller adaptive controller says it is turned off via an external source.
    From what i can see there is Run/Fault indication and an enable signal between the chiller and the BMS, i think the enable signal is sent from the chiller and is interlocked with the pumps.
    Since there is no fault indication on the panel and the pumps are operating and the pressure diff switches are ok, i was wondering if the chiller itself has a flow switch that needs resetting on the controller?

    Any manuals on the controller operation would be appreciated aswell.

    Thanks in advance

    Danny



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47

    Re: Trane chiller problem

    Danny.
    It is just possible that you have a flow switch issue.
    Check out if the attached are relevant?
    Grizzly

    Also I have tried to email you some info but your email address is throwing a wobbly!
    Pm or email me and I will try again with the further info.
    Last edited by Grizzly; 07-04-2010 at 10:26 PM.

  3. #3
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    95
    Rep Power
    20

    Re: Trane chiller problem

    Pm sent Grizzly

    Just to let you know both chillers are doing the same.

    Danny

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Trane chiller problem

    I understand that the units operate automatically RTAA (tracer, novar etc) pumps can be linked with the module I / O and hang time with the connection TB3-3, TB3-4, indicating unemployment is the external


  5. #5
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Trane chiller problem

    Quote Originally Posted by dannycool View Post
    Hi Guys

    We have a pair of Trane RTAA chillers connect to a BMS panel with a Trend controller.
    Whilst i was carrying out maintenance on the pump sets (auto changeover etc) the chillers locked out.
    The chiller adaptive controller says it is turned off via an external source.
    From what i can see there is Run/Fault indication and an enable signal between the chiller and the BMS, i think the enable signal is sent from the chiller and is interlocked with the pumps.
    Since there is no fault indication on the panel and the pumps are operating and the pressure diff switches are ok, i was wondering if the chiller itself has a flow switch that needs resetting on the controller?

    Any manuals on the controller operation would be appreciated aswell.

    Thanks in advance

    Danny
    hi danny,as your chiller is in remote mode,so enable signal coming from remote(heare trend ccontroller) controller(not from adaptive controller).i think this fault due to the mis wiring of trend controller.
    moideen

  6. #6
    Join Date
    Apr 2010
    Location
    UK
    Posts
    6
    Rep Power
    0

    Re: Trane chiller problem

    Danny, the chiller flow switches should be on dedicated terminals and not linked through the enable, which is from the BMS. Have you tried a reset on the BMS as that is your external source?

  7. #7
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    95
    Rep Power
    20

    Re: Trane chiller problem

    Sorted the problem today after a good hour or so tracing wires through a panel which contains the controls for 4 boilers, 2 AHUs, 6 pump sets, 2 chilers, trend system and various other bits of kit and all relays and contactors were unmarked

    Anyway it turned out that i was getting a 115vAC enable signal out of the chiller, through a trend relay, interlocked with the pumps, which were running,so far so good. The circuit was also interlocked with supply AHU which was held off by a belimo damper actuator that had come off its spindle and knocked itself into the closed position.
    Remounted the offending actuator the system burst back into life!
    I was wondering why they would employ the strategy of shutting down the chillers when the AHU is off, because there is also a fan coil circuit aswell?
    Guessing its to do with running the chillers unloaded?

    Regards
    Danny

Similar Threads

  1. Chiller problem
    By Chiller 09 in forum Commercial
    Replies: 9
    Last Post: 17-12-2009, 03:49 PM
  2. Trane chiller
    By Lman in forum Trouble Shooting
    Replies: 4
    Last Post: 13-11-2009, 03:51 PM
  3. trane rtad 125 chiller, reverse phase issue
    By croc1774 in forum Air Conditioning
    Replies: 5
    Last Post: 25-08-2009, 05:44 PM
  4. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •