    Question Dairy cabinet partial ice up



    I have an Austral KM20S1D-1 dairy cabinet that's Icing up the first second thirds of the evap coil but not the centre. All fans are working gas level is OK.?????



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: Dairy cabinet partial ice up

    t/stat prob or defrost ,diff too close,interval too long,dont forget to clean condensor.

  3. #3
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Dairy cabinet partial ice up

    Does it have one evaporator or 2/3 smaller ones?
    lj

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Dairy cabinet partial ice up

    Quote Originally Posted by Pat Milliken View Post
    I have an Austral KM20S1D-1 dairy cabinet that's Icing up the first second thirds of the evap coil but not the centre. All fans are working gas level is OK.?????
    what SST are you running? and defrosts?

    The XM and KM series cases are pretty good and have never really heard of anything like this happening if they are within manufacturers specs, being KM (which are the metric cases) it will have 1 coil
    ...and she said "give it to me you big fridgie"

  5. #5
    Pat Milliken's Avatar
    Pat Milliken Guest

    Re: Dairy cabinet partial ice up

    one evap only

  6. #6
    Pat Milliken's Avatar
    Pat Milliken Guest

    Re: Dairy cabinet partial ice up

    -6 celcius, defrost 3hr for 15 mins

  7. #7
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Dairy cabinet partial ice up

    So 8 defrosts per day @ 15mins, thats as per Austral specs, the -6 is a little low in SST, they are designed for a -3.5 SST at the case (provided you can maintain a constant SST- eg rack system or unloaders on a single system). Running lower can increase the frost load on the case and drop off the airflow, how is the humidity in the shop? Running a lower SST I reckon with 60% and above RH you'd be frosting the coils quickly and losing airflow which it seems you are picking up on the LH and RH ends first.
    ...and she said "give it to me you big fridgie"

  8. #8
    Pat Milliken's Avatar
    Pat Milliken Guest

    Re: Dairy cabinet partial ice up

    Just been to site again and found that one of the AC systems is faulting. Waiting for the AC tech to repair (wty), will advise outcome

  9. #9
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: Dairy cabinet partial ice up

    ah,for every action there is a reaction

  10. #10
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Dairy cabinet partial ice up

    gday pat
    might pay to check superheat setting of your coil also
    cheers
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. small display cabinet keeps seizing up CF motors
    By paul_h in forum Commercial
    Replies: 8
    Last Post: 11-11-2007, 01:56 PM
  2. Duty For costan Dairy cabinet
    By Chris2005 in forum Commercial
    Replies: 1
    Last Post: 12-09-2005, 10:55 PM
  3. Dairy Cabinet
    By iceman007 in forum Commercial
    Replies: 6
    Last Post: 03-07-2004, 11:39 AM
  4. Norpe dairy cabinet
    By iceman007 in forum Commercial
    Replies: 8
    Last Post: 14-06-2004, 10:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •