    Copeland scroll not engaging



    I've just been attempting to commission a R410A ducted 33 kw ducted split system for a warehouse office. The compressor is a copeland scroll when the compressor starts up and the motor runs but the scroll dosen't engage.

    This of course it is one of these stupid copeland scrolls with that annoying high discharge temp safety discs. I understand the reseoning behind them putting it in as a protection.

    But surely on a brand new compressor on a brand new unit it should not cause a problem. Anyway rang the manufactuer of the Unit. You know what they told me, hit the top of the compressor with a mallet to reposition the disc.

    Is this a common problem? Has anyone has a similar expierience?

    I have yet to try the suggest remedy i'll let you know how I go.
    Last edited by fridgey; 30-03-2010 at 12:05 PM. Reason: missing words



  2. #2
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: Copeland scroll not engaging

    i normally swap the phases round and run for 10 secs normally does the trick!

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Copeland scroll not engaging

    Quote Originally Posted by coolhibby1875 View Post
    i normally swap the phases round and run for 10 secs normally does the trick!
    that is 100% correct!!!!!!!!!!!!
    works for me to!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    259
    Rep Power
    21

    Re: Copeland scroll not engaging

    Yep, had the exact same problem, brand new unit compressor starts but does not pump, we changed the compressor, and sent the faulty one back to the supplier, in this case Temperzone in NZ. Unfortunatley the compressor worked on their test bench so they wouldn't cover it. We got it back put it into a second hand unit and test ran it...same thing not pumping, reversed the phases and ran it then put them back and it started pumping, but can we use that compressor again..don't think so..and Temperzone got the sale of another compressor.

  5. #5
    Join Date
    Mar 2008
    Location
    Melbourne, Australia
    Age
    40
    Posts
    48
    Rep Power
    0

    Re: Copeland scroll not engaging

    Haven't been back yet to look at it. Reversing the phases was the first thing I tried with no sucess, so it doesn't always work.

    Goober ironically this unit is a temperzone as well. Maybe this says something!

    I certantly don't want to get stuck with a compressor i can't use. If I cant get it to work i'll definatley be getting there rep out to gaurantee me warranty, before I think of replacing it.

  6. #6
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Copeland scroll not engaging

    If it is a Safety device (ASTP) activating to avoid the compressor failure then you need to find out the root cause. I have experienced this problem at least 4# units and every where I found restriction in the low side like TXV chocking or less refrigerant charge and Low LP set point. After correcting this all those sites were running till now without any problem.

  7. #7
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Copeland scroll not engaging

    Fridgey, If the ASTP has tripped you may need to wait for around 2 hours for it to reset. A common reason for the trip on start up is low charge causing high discharge temps. Try bomb charging the high side (preferably with the correct charge) before start up.