    trane chiller; starter did not transition



    CAN SOMEONE PLS HELP: THE TRANE CENTRIFUGAL CHILLER IS ALWAYS SHOWING THE FOLLOWING ALARM; STARTER DID NOT TRANSITION...the motor starter is a Y delta with transition resistors...

    ragards



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane chiller; starter did not transition

    On all the relais there is a contacter. If one off those is at fault the controller will give the transition fault. If the chiller is set up as part winding instead of Y-delta the same error will come.
    If it ain't broke, don't fix it!

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: trane chiller; starter did not transition

    Quote Originally Posted by oupak View Post
    CAN SOMEONE PLS HELP: THE TRANE CENTRIFUGAL CHILLER IS ALWAYS SHOWING THE FOLLOWING ALARM; STARTER DID NOT TRANSITION...the motor starter is a Y delta with transition resistors...

    ragards
    i thing this is due to control fault.check compressor contactor and its auxilaries.

    Moideen-dubai

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: trane chiller; starter did not transition

    Quote Originally Posted by oupak View Post
    CAN SOMEONE PLS HELP: THE TRANE CENTRIFUGAL CHILLER IS ALWAYS SHOWING THE FOLLOWING ALARM; STARTER DID NOT TRANSITION...the motor starter is a Y delta with transition resistors...

    ragards
    Hi does the chiller go through a contactor check 5 secondes before starting ??
    if it does u have a problem with your auxilary contact that tells the chiller it ended transition .
    if it dosent run the test check your wiring or a burnt coil .
    u could run a test on the staret using the tsest function ,beware to drop the maines before running the test .
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Trane chiller
    By Lman in forum Trouble Shooting
    Replies: 4
    Last Post: 13-11-2009, 03:51 PM
  2. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  3. electric starter panel for chiller
    By Masdede in forum Electrical
    Replies: 2
    Last Post: 26-06-2009, 10:45 AM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •