    Mitsubishi Heavy Industries - Inverter Service Manual.
    Anyone know where i can find a service manual for Mitsubishi Heavy Industries Inverter split systems?
    I have a system that i need to repair but don't know where to start. Indoor fan works and runs but cond fans or compressor don't start.
    I opened up the case and can't see anything visually wrong, threw the gauges on and found that the unit contains the correct refrigerant (R410a).
  2. #2
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    Re: Mitsubishi Heavy Industries - Inverter Service Manual.
    The model number of the FCU is SRK712EA-S1.
    The outdoor unit has no info on it.
  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Are you sure in your model#?
    How old is that?
  4. #4
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    you must have posted that just as i posted the model number
  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by bundysnake View Post
    Jep!
    It shuld be SRK 71 ZEA-S1!
    Correct?
  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
  7. #7
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    yea thats the correct model number, is there any other pages? that one doesn't tell me a great deal.
    The indoor fan runs perfect, but no outdoor fan or compressor.
  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Check error codes as described there!
  9. #9
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    There is no error codes on that image. it says to refer to page 121.
  10. #10
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19
    Will this help you
    http://www.abacusairconditioning.co....lt%20Codes.pdf
    My wife used to say you never listen to a word I say at least I think that what she said
  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    You should first enter service mode to show error codes as described at image I posted. Than post your findings here.
  12. #12
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    Thanks nike123 & Toosh, i will post my findings here.
    Does anyone have a complete service manual for this unit i can download & print? or know where i can obtain one?
  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Try here!
    Still, it would be good to post your findings here even if you find manual.
  14. #14
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    thanks for the link nike123 but i can't access them as im not a member and i can't speak that language. If ipm you my email could you send me the manual for the unit please?
  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Use Google translate and develop some search skills!
    http://translate.google.com/translat...eavy.php&twu=1
    Apply for registration!
    You youngsters are always expecting everything on plate.
  16. #16
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19
    why not go back to the mob who you got it from.im assuming actrol its strange that they cant help you out.
    on that mandatory fact sheet it should also list have you googled it
    mmm to beer or not to beer...........lets drink breakfast
  17. #17
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    lowcool i didn't buy the unit, i just got the service call.
    What is this mandatory fact sheet you speak of?
  18. #18
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19
    gday bundy
    the fact sheet is a topic for suggestions for the forums.im not 100% clued up on back up from actrol but have found a fellow here called tony nighberg at the marleston store to be rather helpful.ive installed a few but as yet have not had go down the road you are now.happy fault finding fella.
    cheers
    sorry if ive misspelt your surname tony
  19. #19
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19
    Hi Bundy this is handy to have Fault Codes
    http://www.abacusairconditioning.co....ult-Codes.html
    Toosh
  20. #20
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    Ok so what i found after attemptimg to get the unit in service mode.
    LEDS on FCU flashed
    2 x run +timer
    2 x timer
    1 x run + timer + econ
    does anyone know what this means?
    I'm starting to think i need to get a mitsubishi service person out there?
    There were no codes displayed on the remote control, i attempted the service mode display procedure around 10 times.
    Any help would be appreciated.
  21. #21
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    can anyone help?
  22. #22
    Join Date
    Jun 2009
    Location
    Sydney
    Posts
    70
    Rep Power
    16
    how old is the system? as its a 71ZEA i would assume its still under its warranty (5 year residential, 3 year commercial)? If so get their service agent out
  23. #23
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    The customer doesn't have any proof of purchase or anything as he bought his business with the air cons installed.
    He might just have to pay for a mitsubishi service agent to go out there.
  24. #24
    Join Date
    Jun 2009
    Location
    Sydney
    Posts
    70
    Rep Power
    16
    Oh thats a pity, I thought it may have been a little lifeline for you. Although it is always beneficial to be able to sort out the problem for our own knowledge!
  25. #25
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19
    Hi call the company that sold this unit ,as they have records of who & when bought this unit ,just try and find the serial no'
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
  26. #26
    Join Date
    Feb 2005
    Location
    london
    Posts
    32
    Rep Power
    0
    i dont know if this is the same but i think it is
    when you open the top is the pcb upside down if yes there is another board under there this is the inverter driver and runs the fan
    i have had 3 of these die after a year or so in service
  27. #27
    Join Date
    Mar 2007
    Location
    manchester
    Age
    17
    Posts
    63
    Rep Power
    19
    i had two of these pcb that drives fan /inverter fail
  28. #28
    Join Date
    Apr 2005
    Location
    dorset uk (Brisbane) now
    Age
    53
    Posts
    22
    Rep Power
    0
    there is a hidden fuse on the inverter board this board is upside down it will need replacing(the pcb) . i had the same problem on a unit order all the outdoor pcb's to find only inverter pcb needed
  29. #29
    Join Date
    Oct 2009
    Location
    Aust
    Age
    39
    Posts
    49
    Rep Power
    0
    Thanks for all you help everyone
    I found a great link to the service handbook. http://www.mhiaa.com.au/docs/MHIAA_P...de_Book_A5.pdf
    The fault im getting is error 22 which is outdoor pcb so im guessing it just the inverter pcb. I will order it and see how i go.
    Anyone got any pointers how to replace these things? and do they hold any residual voltage i should be aware of?
  30. #30
    Join Date
    Aug 2008
    Location
    germany
    Posts
    34
    Rep Power
    0
    Hi everybody,
    the question of checking error codes reminds me of something I have been wondering about with Mitsubishis small splits (like the SRK25ZJX-S):
    Is there a simple way to put the units in forced cooling for pump down?
    None of the mitsubishi service manuals mentions this; those of any other manufacturer do.
    Cheers,
    -Dave
  31. #31
    trandovn's Avatar
    trandovn Guest
    I come from VN. I readed the comemt of everybody. thanks so much. I just download MHI techniacal manual. I really need.
  32. #32
    gnasch's Avatar
    gnasch Guest
    Citing from Indoor Unit Installation Manual RKY012A007A:
    Forced cooling operation
    Turn on a power supply again after a while after turn off a power supply. Then press continually the ON/OFF button 5 seconds or more
    hope this helps,
    gnasch
Similar Threads
  1. mitsubishi heavy industries fault
    By skeggyboy in forum Air Conditioning
    Last Post: 20-08-2009, 06:41 PM
  2. Mitsubishi Heavy Industries FDC2501 tech advice required
    By aeaves in forum Air Conditioning
    Last Post: 20-04-2009, 08:44 AM
  3. Mitsubishi Heavy Industries service software
    By nike123 in forum Air Conditioning
    Last Post: 03-12-2008, 11:30 PM
  4. vrf- Mitsubishi heavy industries
    By kerrcell in forum Air Conditioning
    Last Post: 25-05-2008, 11:57 AM
  5. Mitsubishi Heavy Industries
    By Freecool in forum Air Conditioning
    Last Post: 17-08-2007, 03:20 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts