    Water heat pump



    Hi all! I am busy building a domestic water heater with a 2,5kw split air conditioner compressor unit using R22 gas. Could anyone help me with the sizing of the condenser (the heater) I have used about 9 metres of 1/4 inch copper tubing which I have coiled up to fit into the water storage tank (150l) The problem I am having is that the high pressure side is going up to 500psi. I am guessing 200 -250psi would be acceptable? The unit is heating quiet well. Do I make the condenser bigger, or do I shorten the capillary tube? When the unit is running the condenser only feels hot about half way up.Could anyone advise me on this?



  2. #2
    Join Date
    Apr 2009
    Location
    Australia
    Age
    61
    Posts
    30
    Rep Power
    0

    Re: Water heat pump

    At 250psi i'd suspect your water temperature is only going to be around 38-40degC on r22. If you go higher in water temperature then your compressor will fail on thermal overload due to high current draw. Try using 3/8-1/2 copper for your condenser coil. If you want a sloppy method of calculating your condenser length then measure and count the rows on your evaporator, then add 20%. Your experiment will fail using R22 with that compressor.

    I'd suggest replacing the TXV or capillary and changing your refrigerant to 134a, and dont set the thermostat beyond 50degC. The capilary tube needs to match your compressor capacity on the chosen refrigerant.

    Monitor the compressor current draw when charging the unit, rather then the suction pressure/temperature. Check the current draw again as the water temp approachs SP.

    Your PT chart and Tong tester will be your best friends on this experiment.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Water heat pump

    Quote Originally Posted by Cool Mike View Post
    Hi all! I am busy building a domestic water heater with a 2,5kw split air conditioner compressor unit using R22 gas. Could anyone help me with the sizing of the condenser (the heater) I have used about 9 metres of 1/4 inch copper tubing which I have coiled up to fit into the water storage tank (150l) The problem I am having is that the high pressure side is going up to 500psi. I am guessing 200 -250psi would be acceptable? The unit is heating quiet well. Do I make the condenser bigger, or do I shorten the capillary tube? When the unit is running the condenser only feels hot about half way up.Could anyone advise me on this?
    Your tubing coil (heater) should be a de-superheater, not a condenser.

    In other words, the discharge gas should go through the tubing coil and then through an air cooled condenser.

    Use a pressure switch on the condenser fan to limit high side pressure.

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Water heat pump

    First use TXV.
    Remember that the water is static in the cylinder (very poor heat transfer)
    So for coil sizing look at 60Btu/Ftsqu/f
    Let you convert to SI units.
    Actual configuation we all have our own secrets

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Water heat pump

    Talk to des A, he is a guru on air to water heat recovery.
    As per Gary's suggestion, desuperheating is inefficient. Max 15 > 20% of total heat of rejection to maintain compressor operating conditions.
    R22 is not the best option either, consider R410A. Add water regeneration and cycle water discharge on loop temp

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Water heat pump

    Quote Originally Posted by Magoo View Post
    Talk to des A, he is a guru on air to water heat recovery.
    As per Gary's suggestion, desuperheating is inefficient. Max 15 > 20% of total heat of rejection to maintain compressor operating conditions.
    ... when the condenser fan is running.

    When the condenser fan is not running, the de-superheater becomes a condenser.

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Water heat pump

    Quote Originally Posted by Magoo View Post
    Talk to des A, he is a guru on air to water heat recovery.
    I'm honoured... We all stand on the shoulders of giants... Gary, Magoo, Mad-Fridgie, Chef... the giant's list is long

    For reference:
    1 Btu/(h.ft2.'F)=5.677 W/(m2.'C)=5.677 W/(m2.K)

    Water-side coil heat-transfer coefficient, as per mad_fridgie:
    60 Btu/(h.ft2.'F)=340.62 W/m2.K

    Personally, I'd think that this could be a little on the high side for a tank internal coil, with unmixed water. The heat-transfer here will be restricted by the water-side natural convection, which, at best, will have a heat-transfer coefficient of around 5-10 W/m2.K

    Tank internal coil:
    With a refrigerant condensation coefficient of say 1000W/m2.K (well to the upper end, I'd expect - rough ballpark), the expected coil/water combined heat-transfer would be around (neglecting wall loss & fouling):

    R,eq = (hi+ho)/(hi*ho) = (1000+10)/(1000*10)=0.101 m2.K/W

    U,eq=1/R,eq=1/0.101 = 9.9 W/m2.K !!! (ie. aweful)

    Next:
    Apply small water pump to circulate the tank contents - mixed-mode, slightly-forced convection, heat-transfer:

    ho~50 W/m2.K

    R,eq = (hi+ho)/(hi*ho) = (1000+50)/(1000*50)=0.021 m2.K/W

    U,eq=1/R,eq=1/0.021 = 47.62 W/m2.K !!! (getting better)

    Next - again:
    Apply small water pump to circulate the tank contents through a decent water-cooled condenser:

    ho~5000 W/m2.K (water-side, conservative)

    R,eq = (hi+ho)/(hi*ho) = (1000+5000)/(1000*5000)=0.0012 m2.K/W

    U,eq=1/R,eq=1/0.0012 = 833.33 W/m2.K !!! (are we there yet?)
    Last edited by desA; 17-10-2009 at 03:44 AM. Reason: re-named h,eq to U,eq = overall heat-transfer coefficient
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Water heat pump

    As the patent holder of the worlds highest efficient hot water heat pumps (SFT and Boost) "probably as carlsberg would say", I can say R22 is an acceptable refrigerant, especially as you already have the unit.
    You need to look at the evap configuration (it is more than likely configured as a condensor) Your are more than likely need to increase the number of circuits. (evap pressure drop)
    This should give a higher SST, allowing you to increase your SCT (compression ratios)
    The condensor top feed, do not worry if you over size, you can use as a type of reciever/ liquid sub cooler. You could use a small "p" trap to ensure a liquid seal. Control can be based upon temp and HP The HP cut should be under maximum rating for the compressor type for example if max rating is 65C then have it at 60C.

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Water heat pump

    Quote Originally Posted by mad fridgie View Post
    As the patent holder of the worlds highest efficient hot water heat pumps (SFT and Boost)
    http://www.sft.no/arbeidsomr/luft/ku...samlet_eng.pdf

    An interesting link to the word SFT...

    Probably totally out of context. You wouldn't be using ammonia for your heat-pump, would you?
    Last edited by desA; 17-10-2009 at 04:18 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  10. #10
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Water heat pump

    Hi DesA, a little conservative but natural convection in a cylinder always an issue as far as heat transfer, For this particular application based upon heat of rejection of 3kw I would look at at installing 39 lineal meters of 15mm (1/2inch).
    Do not generally do static for the above reasons (variable heat transfer coefficients), internal mixing of the cylinder in my option is a no no, best use natural stratification.
    Certainally I prefer the pump method, so what more predicatable.
    I applogise for swapping between imperial and SI units (static coils I can only remember in imperial unit)

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Water heat pump

    Quote Originally Posted by desA View Post
    http://www.sft.no/arbeidsomr/luft/ku...samlet_eng.pdf

    An interesting link to the word SFT...

    Probably totally out of context. You wouldn't be using ammonia for your heat-pump, would you?
    Well found, Is not funny how search engines find differnt infomation depending where you are searching from! Maybe i need to change the name,
    No not using ammonia, the process could accept ammonia, but I do not think i could make one for a price that i could ever sell (domestic size)

  12. #12
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Water heat pump

    ^ lol...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  13. #13
    Join Date
    Mar 2010
    Location
    guangzhou
    Posts
    7
    Rep Power
    0

    Re: Water heat pump

    Buy an set of air source heat pump or take the r417a in to consideration.... @_@

Similar Threads

  1. Advice required Air / Water heat pump systems
    By oddjob1607 in forum Heat Pumps
    Replies: 8
    Last Post: 13-12-2010, 07:48 PM
  2. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  4. VFD heat pump water heater?
    By star882 in forum New Technologies
    Replies: 0
    Last Post: 23-05-2006, 08:36 PM
  5. Water Source Heat Pump
    By aliugur in forum Fundamentals
    Replies: 1
    Last Post: 02-06-2002, 03:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •