    Angry Pump for flooded evaporator



    Help!!
    How to calculate volume flow of the pump for
    R-507 for flooded evaporator W=400kW, -40 C



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Pump for flooded evaporator

    Calculate amount of refrigerant flow through compressor and usually multiply by 4 for a 4 to 1 curculation ratio .

    ie ciculate 4 kg refrigerant and only 1 kg turns to gas as a rough rule .

    You may have to find out evaporator design circulation rate .

    If its only 1 evaporator you may have a problem as pumps of this style could be way to big if small evaporator
    Last edited by RANGER1; 24-02-2010 at 08:40 AM.

  3. #3
    Join Date
    Aug 2008
    Location
    California
    Posts
    28
    Rep Power
    0

    Re: Pump for flooded evaporator

    The long answer…


    Find the R-507 thermodynamic tables

    Look up suction vapor enthalpy value
    Look up the liquid feed enthalpy valve

    Subtract the liquid enthalpy from the vapor enthalpy
    This is your refrigeration effect

    Divide your desired load (400kw) by the refrigeration effect
    This is your mass flow rate

    Divide your mass flow rate by your liquid density
    This is your raw volumetric flow rate

    Multiply your raw volumetric flow rate by the recirculation rate (say 4 for flooded)
    This is the amount you need to pump.

  4. #4
    Join Date
    Apr 2009
    Location
    Israel
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: Pump for flooded evaporator

    How much Pump Circulation Rate
    should be ?


  5. #5
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Pump for flooded evaporator

    Circulation rate is a function of the circuit design within the evaporator. I've seen as low as 1.1 to 1 and as high as 5 to 1. 3 to 1 and 4 to 1 are most common for air cooling evaporators.

  6. #6
    Join Date
    Apr 2009
    Location
    Israel
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: Pump for flooded evaporator

    Quote Originally Posted by charlie n View Post
    Circulation rate is a function of the circuit design within the evaporator. I've seen as low as 1.1 to 1 and as high as 5 to 1. 3 to 1 and 4 to 1 are most common for air cooling evaporators.
    Thanks, but what is better for shock freezing -40C?

  7. #7
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Pump for flooded evaporator

    Probably 4:1 is the most common recirculation rate. Ask your evaporator coil manufacturer. For example, one of the Canadian manufacturers makes down fed aluminum evaporators using 5:1 so it really depends on the evaporator design.

  8. #8
    Join Date
    Aug 2008
    Location
    California
    Posts
    28
    Rep Power
    0

    Re: Pump for flooded evaporator

    Remember R-507 is expensive, going 4-1 means you need to have a larger pipe to reduce the friction losses though the pipe. Also you will have a larger refrigerant charge. Your evaporator efficiency will go up with 4-1 but so will your costs. consider economizing on the liquid feed to say 2-1 or 3-1. This may save you money in the long run.

  9. #9
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Pump for flooded evaporator

    Better still, build the freezer for ammonia.

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pump for flooded evaporator

    Hi Decosta.
    very good explantion of what happens and what is required.
    magoo
    Last edited by Magoo; 01-03-2010 at 01:15 AM.

  11. #11
    Join Date
    Apr 2009
    Location
    Israel
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: Pump for flooded evaporator

    Quote Originally Posted by charlie n View Post
    Better still, build the freezer for ammonia.
    Unfortunately there is no permission

  12. #12
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Pump for flooded evaporator

    I remember being told that about a skating rink installation in your country but I had hoped the authorities would have seen the light in the case of an industrial situation. Unfortunately not.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. EVAPORATOR leaked
    By James priyono in forum Air Conditioning
    Replies: 4
    Last Post: 23-05-2009, 10:19 AM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  5. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Replies: 7
    Last Post: 20-03-2006, 02:26 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •