    daikin indorr unit flashing error of hj



    i need help with a error code coming up error code is HJ unit 0 cant find it anywhere really need some help

    thanks
    pringy01



  2. #2
    Join Date
    Feb 2010
    Location
    wales
    Posts
    6
    Rep Power
    0

    Re: daikin indorr unit flashing error of hj

    the unit is a
    WATER COOLED VRV
    with 4
    Round flow cassette
    fans

  3. #3
    Join Date
    Feb 2010
    Location
    wales
    Posts
    6
    Rep Power
    0

    Re: daikin indorr unit flashing error of hj

    if it helps the code number is
    rweyq8p 3 please help !!!!!!!!

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: daikin indorr unit flashing error of hj

    HJ Outdoor unit · water system fault

    Check the water circulation system; pump, air locks, flow switch etc.
    Last edited by Brian_UK; 24-02-2010 at 10:56 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2010
    Location
    wales
    Posts
    6
    Rep Power
    0

    Re: daikin indorr unit flashing error of hj

    thats great thanks but would it be the same error on the water cooled vrv with the code number of rweyq8p???? thanks

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daikin indorr unit flashing error of hj

    Quote Originally Posted by pringy01 View Post
    i need help with a error code coming up error code is HJ unit 0 cant find it anywhere really need some help

    thanks
    pringy01
    Hi,

    As Brian said, this error is due to lack of water flow <50 l/m or flow switch is open circuit during operation.

    • Do the units have flow switches installed? Are they working correctly?
    • Are the units and pumps controlled independently? If so verify the units are never enabled unless pumps are operating.
    • Do the units have a water strainer installed on every plate heat exchanger inlet (1 per unit)? Have you checked the strainers are clean? If there are no strainers installed you will have no warranty and the plate heat exchangers could be partially blocked.
    • Do you have the correct water flow through all units? Have pumps been correctly sized, flow rates checked and balanced (nominal flow rate is 96 l/m per unit)?
    • I would suggest you check the heat exchanger inlet/outlet water ΔT this should be between 3~8 C when unit is operating at 100% capacity, if the ΔT is >8 C the flow rate is insufficient.
    • Also check the inlet water temperature is within the continual operating range 15~35 C.
    Last edited by VRVIII; 25-02-2010 at 12:14 PM.

  7. #7
    Join Date
    Feb 2010
    Location
    wales
    Posts
    6
    Rep Power
    0

    Re: daikin indorr unit flashing error of hj

    Thanks for the responsise to the error codes they are very helpfull there is a flow switch on the system but the main contractor still hasnt wired it up has just linked it out within the unit. Would you agree that is the main issue i have on the system

    thanks again

  8. #8
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daikin indorr unit flashing error of hj

    Quote Originally Posted by pringy01 View Post
    Thanks for the responsise to the error codes they are very helpfull there is a flow switch on the system but the main contractor still hasnt wired it up has just linked it out within the unit. Would you agree that is the main issue i have on the system

    thanks again
    I would say the issue is defiantly low water flow this is being detected by the heat exchanger refrigerant thermistor as the flow switch is linked out.
    The flow switch must be connected across terminals 3 & 4 of terminal block X2 this is used as a safety device to protect the plate heat exchangers.
    The system must not be operated until you have rectified the low water flow. Continually resetting this fault can result in freezing of the plate heat exchanger which can fracture the internals or compressor failure due to liquid pumping.




    I would suggest you verify the point I mentioned in previous post,
      • Do the units have flow switches installed? Are they working correctly?
      • Are the units and pumps controlled independently? If so verify the units are never enabled unless pumps are operating.
      • Do the units have a water strainer installed on every plate heat exchanger inlet (1 per unit)? Have you checked the strainers are clean? If there are no strainers installed you will have no warranty and the plate heat exchangers could be partially blocked.
      • Do you have the correct water flow through all units? Have pumps been correctly sized, flow rates checked and balanced (nominal flow rate is 96 l/m per unit)?
      • I would suggest you check the heat exchanger inlet/outlet water ΔT this should be between 3~8 C when unit is operating at 100% capacity, if the ΔT is >8 C the flow rate is insufficient.
      • Also check the inlet water temperature is within the continual operating range 15~35 C.
      25-02-2010 07:52 AM

  9. #9
    Join Date
    Feb 2010
    Location
    wales
    Posts
    6
    Rep Power
    0

    Re: daikin indorr unit flashing error of hj

    many thanks on this subject has all been takin in and hopefully resolv the situation

    thanks again

Similar Threads

  1. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  2. Daikin a/c units.
    By rick in forum Air Conditioning
    Replies: 59
    Last Post: 18-02-2008, 09:22 PM
  3. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  4. Daikin Indoor Unit