    Exclamation Mitsubishi Close Control



    I have two 60kW Mitsubishi Close Control unit in a data room that are tripping out the compressors at low ambient temperature. No faults are showing on the controllers or mitsubishi laptop. Mitsubishi cant give me a reason, anybody any ideas.?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Mitsubishi Close Control

    When you say "tripping out the compressors" what exactly do you mean?

    Is the power MCB tripping, is the compressor klixon tripping, etc?

    Also, the model number would be helpful.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi Close Control

    Can you look at the fault history record at the outdoor unit to see if there are any preliminary faults.

    Preliminary faults are not displayed at the remote controller & can sometimes give an idea what might be the problem.

    Do the compressors restart after a period of time or only after power reset ?

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Mitsubishi Close Control

    Quote Originally Posted by techni View Post
    I have two 60kW Mitsubishi Close Control unit in a data room that are tripping out the compressors at low ambient temperature. No faults are showing on the controllers or mitsubishi laptop. Mitsubishi cant give me a reason, anybody any ideas.?
    Are these downflow PFD-P500VM-E indoor units with 2 x PUHY-P250YHM-A outdoor units?
    If so the Tech manuals for these are on the 2009 Mitsi Tech CDROM. These manuals are large (over 180 pages).
    Check the minimum outdoor operating temp for these systems with Mitsi (I couldn't find any info in the stuff I had). If the min ambient operating temp in cooling for these systems is only -5c then this will be your problem in the cold weather we are currently experiencing. There's probably a suction line, evap or ambient sensor somewhere that's locking out or holding off the compressor. However, it's strange that no error code is displayed to inform you of this. Stranger that Mitsi could not offer any detailed info!!
    With a bit of luck a Mitsi specialist will offer some further advise on this site shortly.
    We've had quite a few call outs recently on splits on server rooms that have stopped cooling operation due the low ambient temps. Most systems are good for -5c ambient in cooling mode but -15c is the normal requirement for UK applications. Having said that Oxford & Scotland saw -17c & -20c respectively recently so even systems capable of operating down to -15c would have been in trouble. Even some of the specialist DX close control systems (Airedale & the like) won't run below -15c / -20c without special modifications.
    Good luck.
    If in doubt read the instructions. If still in doubt follow them.

  5. #5
    Join Date
    Aug 2001
    Location
    ireland
    Posts
    34
    Rep Power
    0

    Re: Mitsubishi Close Control

    Sorry for late reply but I have been out of action due to illness, Mitsubishi put the problem down to software and upgrade this so that the units ran. When the unit did'nt cool at low ambient the compressors still ran , just did'nt cool the room, we had temperatures of -10 with a wind chill of -25. I presume they upgraded the software to run at a lower ambient.

  6. #6
    Join Date
    Aug 2009
    Location
    ireland
    Posts
    12
    Rep Power
    0

    Re: Mitsubishi Close Control

    I only heard today that the indoor unit software must be updated, the wrong software was installed, check, below v1.03 must be updated.

Similar Threads

  1. Leak on Airedale Close Control, Help!!
    By Bash1803 in forum Air Conditioning
    Replies: 19
    Last Post: 29-09-2009, 09:23 AM
  2. Close Control Definition
    By 2aces in forum Air Conditioning
    Replies: 3
    Last Post: 28-01-2009, 10:09 PM
  3. wall mounted close control
    By dannycool in forum Air Conditioning
    Replies: 15
    Last Post: 25-01-2009, 07:36 PM
  4. Central control Mitsubishi
    By multisync in forum Air Conditioning
    Replies: 6
    Last Post: 19-08-2008, 06:25 AM
  5. Mitsubishi Mr slim outdoor fan control
    By Blackbird in forum Air Conditioning
    Replies: 3
    Last Post: 01-07-2008, 08:20 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •