Results 1 to 13 of 13
Thread: Expansion Valve Selection
Threaded View
-
15-02-2010, 11:47 AM #11
Re: Expansion Valve Selection
You will also need an oil separator in case if you switch off one compressor & operate only one compressor with 50% evap load because your suction line is not designed for part load condition .
( on 50% evap load , oil return becomes a problem)