Kevry open display case freezing up
Have a open display case that has the air curtain on it.
Unit is 404a
Suction 55
Suction line 54
superheat 34
discharge 280
line temp 108
subcooling 6
Has a sporlan temp contol on it. Set unit to 30 keeps things at 39 to 40.
Unit will run for a week then freeze up. Does anyone know about sporlan electronic temperature controls.
-
28-07-2009, 03:32 AM #2
Re: Kevry open display case freezing up
Being from the usa, let's assume F and PSI. Can we also assume TXV system? Is this a single compressor system or connected to a rack? Is the condenser outdoors?... or under the cabinet?... or perhaps it is water cooled?
We can't see it from here. Paint us a picture.
-
28-07-2009, 03:46 AM #3
Re: Kevry open display case freezing up
Glad you chimed in.
txv, and condenser is under unit and it is inside, and sorry psi and f
-
28-07-2009, 03:49 AM #4
Re: Kevry open display case freezing up
this is what it looks like
http://www.kevry.com/html/product_page.php?prod=29
-
28-07-2009, 03:55 AM #5
Re: Kevry open display case freezing up
If we assume 75F room temperature, then the SCT is running about 39F over ambient. So I'm thinking the condenser is probably dirty, but then... 75F room air is just an assumption. It would be good to know the condenser air in and air out temps. If cleaning the condenser doesn't do it, then it probably has a leak.
-
28-07-2009, 09:51 AM #6
Re: Kevry open display case freezing up
condenser is clean, the place is about 70f. Did not check the in out temp will do and let you know.
-
08-02-2010, 02:08 AM #7
Re: Kevry open display case freezing up
Faulty Evaperator fan can cause the freeze up, as well as a Low charge. I've seen the fans start then stop. Usually catch one going bad by accident. Clogged condensors are big in my buisness...where the cutomers doesnt want dust blown anywhere around the food on display.
-
08-02-2010, 03:21 AM #8
Re: Kevry open display case freezing up
Good grief. I had a case haunt me for months with ice up problems off and on.
Store would shut it down to defrost it 3 or 4 times, then call us.
We finally tracked the problem down to a faulty defrost controller.
By "Sporlan temperature controller" Do you mean the Omnistat or a different one?
Check everything on the refrigeration side twice, THEN, if you find nothing, replace that controller.
-
08-02-2010, 07:22 AM #9
Re: Kevry open display case freezing up
Any possibility that an evap fan may have been changed recently? if so check rotation and blade attitude.
Similar Threads
-
Help needed sourcing insulation for a Display Case
By jimbo22 in forum Technical SpeculationsReplies: 2Last Post: 03-11-2008, 09:30 AM -
a frozen book display case
By tempo in forum Technical DiscussionsReplies: 3Last Post: 15-08-2008, 07:20 PM -
Zoin Chocolate display case
By Andy AC in forum CommercialReplies: 0Last Post: 04-05-2008, 02:02 PM -
Two temperature display case with low suction presure
By kengineering in forum Supermarket RefrigerationReplies: 11Last Post: 05-03-2007, 02:13 PM -
Fogal Open Display Case
By Abe in forum CommercialReplies: 2Last Post: 07-05-2005, 08:47 PM