    Kevry open display case freezing up



    Have a open display case that has the air curtain on it.

    Unit is 404a

    Suction 55
    Suction line 54
    superheat 34

    discharge 280
    line temp 108
    subcooling 6

    Has a sporlan temp contol on it. Set unit to 30 keeps things at 39 to 40.

    Unit will run for a week then freeze up. Does anyone know about sporlan electronic temperature controls.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Kevry open display case freezing up

    Being from the usa, let's assume F and PSI. Can we also assume TXV system? Is this a single compressor system or connected to a rack? Is the condenser outdoors?... or under the cabinet?... or perhaps it is water cooled?

    We can't see it from here. Paint us a picture.

  3. #3
    Join Date
    Jul 2009
    Location
    usa
    Age
    47
    Posts
    24
    Rep Power
    0

    Re: Kevry open display case freezing up

    Glad you chimed in.

    txv, and condenser is under unit and it is inside, and sorry psi and f

  4. #4
    Join Date
    Jul 2009
    Location
    usa
    Age
    47
    Posts
    24
    Rep Power
    0

    Re: Kevry open display case freezing up


  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Kevry open display case freezing up

    If we assume 75F room temperature, then the SCT is running about 39F over ambient. So I'm thinking the condenser is probably dirty, but then... 75F room air is just an assumption. It would be good to know the condenser air in and air out temps. If cleaning the condenser doesn't do it, then it probably has a leak.

  6. #6
    Join Date
    Jul 2009
    Location
    usa
    Age
    47
    Posts
    24
    Rep Power
    0

    Re: Kevry open display case freezing up

    condenser is clean, the place is about 70f. Did not check the in out temp will do and let you know.

  7. #7
    Join Date
    Sep 2008
    Location
    Chicago, IL.
    Posts
    6
    Rep Power
    0

    Re: Kevry open display case freezing up

    Faulty Evaperator fan can cause the freeze up, as well as a Low charge. I've seen the fans start then stop. Usually catch one going bad by accident. Clogged condensors are big in my buisness...where the cutomers doesnt want dust blown anywhere around the food on display.

  8. #8
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    49
    Posts
    69
    Rep Power
    15

    Re: Kevry open display case freezing up

    Good grief. I had a case haunt me for months with ice up problems off and on.

    Store would shut it down to defrost it 3 or 4 times, then call us.

    We finally tracked the problem down to a faulty defrost controller.

    By "Sporlan temperature controller" Do you mean the Omnistat or a different one?

    Check everything on the refrigeration side twice, THEN, if you find nothing, replace that controller.

  9. #9
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    18

    Re: Kevry open display case freezing up

    Any possibility that an evap fan may have been changed recently? if so check rotation and blade attitude.

Similar Threads

  1. Help needed sourcing insulation for a Display Case
    By jimbo22 in forum Technical Speculations
    Replies: 2
    Last Post: 03-11-2008, 09:30 AM
  2. a frozen book display case
    By tempo in forum Technical Discussions
    Replies: 3
    Last Post: 15-08-2008, 07:20 PM
  3. Zoin Chocolate display case
    By Andy AC in forum Commercial
    Replies: 0
    Last Post: 04-05-2008, 02:02 PM
  4. Two temperature display case with low suction presure
    By kengineering in forum Supermarket Refrigeration
    Replies: 11
    Last Post: 05-03-2007, 02:13 PM
  5. Fogal Open Display Case
    By Abe in forum Commercial
    Replies: 2
    Last Post: 07-05-2005, 08:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •