    Daikin have heatpump but can not set up auto mode (^_^)



    hi, every one !!!
    i have an problem that need to be fix in short time .
    i am an Engineer from Viet Nam .
    i am using remote controller model:BRC1C61 for a VRV3 system which have heat pump mode .
    Issue 1: i try to setup it to 'auto' mode but when i press 'OPERATION MODE 'SELECTOR BUTTON ' . It just display 'dry', 'cool', 'heat', 'fan' .i can not find 'auto' mode? what is this problem ...?
    Issue 2: In this model can i set up 'max' and 'min' temperature ? please, guide me if it can ... (^_^)

    CONGRATULATED THE OUR FORUM ON MORE SUSTAINABLE DEVELOPMENT
    Thanks and best regard



  2. #2
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    17

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    did you say its a 3 pipe system,if its a two pipe system you wont get auto up on the remote

  3. #3
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    Quote Originally Posted by vietvho View Post
    hi, every one !!!
    i have an problem that need to be fix in short time .
    i am an Engineer from Viet Nam .
    i am using remote controller model:BRC1C61 for a VRV3 system which have heat pump mode .
    Issue 1: i try to setup it to 'auto' mode but when i press 'OPERATION MODE 'SELECTOR BUTTON ' . It just display 'dry', 'cool', 'heat', 'fan' .i can not find 'auto' mode? what is this problem ...?
    You need to change field setting on outdoor PCB, mode 3 setting 3 binary 2 this will allow auto change over.
    Issue 2: In this model can i set up 'max' and 'min' temperature ? please, guide me if it can ... (^_^)
    You would need to install an I Touch controller to allow temp limits to be set. It may also be possible with new BRC1E type controllers but you would need to check this with Daikin.

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    You need to change field setting on outdoor PCB, mode 3 setting 3 binary 2 this will allow auto change over.

    Hi VRVIII and how are you...?
    I know some settings in mode 3... and i don't understand what it mean in your answer, can you please explain more..
    Kind regards
    cool#9

  5. #5
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    don't have any one wanna help me ???
    ohh !!!


    i really cannot fix this problem , please !!!
    "my VRV3 system have 2 pipe , and have both heating ,cooling"


    Thank a lot and Kind regard !!!

    Have good time , my friends !!!

  6. #6
    Join Date
    Aug 2009
    Location
    east anglia
    Age
    49
    Posts
    95
    Rep Power
    15

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    Quote Originally Posted by ballvalve View Post
    did you say its a 3 pipe system,if its a two pipe system you wont get auto up on the remote

  7. #7
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    Quote Originally Posted by croc1774 View Post

    did you say its a 3 pipe system,if its a two pipe system you wont get auto up on the remote
    I disagree and think you will find it is possible!
    You need to change field setting on outdoor PCB, mode 3 setting 3 binary 2 this will allow auto change over.
    Providing the system is set for indoor heat/cool changeover (DS1/1 OFF)
    Enter setting mode 3 (mode+return for 5secs)
    Setting 3 (press set x 3 then return x 1)
    enable auto (press set x 1 then return x 2)
    exit setting mode (mode x 1)

    The controller connected to the heat/cool master indoor will have auto change over available, all others can only change between operation mode of master and fan only.

    Last edited by VRVIII; 31-01-2010 at 09:21 AM.

  8. #8
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    Quote Originally Posted by VRVIII View Post
    I disagree and think you will find it is possible!

    Providing the system is set for indoor heat/cool changeover (DS1/1 OFF)
    Enter setting mode 3 (mode+return for 5secs)
    Setting 3 (press set x 3 then return x 1)
    enable auto (press set x 1 then return x 2)
    exit setting mode (mode x 1)

    The controller connected to the heat/cool master indoor will have auto change over available, all others can only change between operation mode of master and fan only.


    After you have Auto shown on the remote controller don't you have to set the field code on at the remote to 12-4-x? The final code of x = 1 through 8 for the change over differential between Heating and Cooling. The default factory setting is 1 which is a 0*C differential and each number higher on the setting is 1*C more differential. If you make no change to the field setting then the heating and cooling temps will be maintained the same with a 0*C differential.

  9. #9
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin have heatpump but can not set up auto mode (^_^)

    Quote Originally Posted by mchild View Post
    After you have Auto shown on the remote controller don't you have to set the field code on at the remote to 12-4-x? The final code of x = 1 through 8 for the change over differential between Heating and Cooling. The default factory setting is 1 which is a 0*C differential and each number higher on the setting is 1*C more differential. If you make no change to the field setting then the heating and cooling temps will be maintained the same with a 0*C differential.
    Hi Mchild,
    Yes the above is correct but this will only have effect on H/C master controller.

  10. #10
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Ohhh !!! So great

    I Fixed my problem to day !!! OH OH !!!
    Thank a lot my friends !!!
    You are wonderful Engineer !!!
    I think our forum will be develop very good !!!
    Special thanks to you VRVIII , You are so great !!!
    Have a beautiful time and hope we will have more and more discus for advance our knowledge !!!


    Finally,
    Thank our forum !!!
    Thank my friend and best wish !!!

    SO GREAT !!!
    SO FUN !!!
    SO HAPPY !!!
    BEST REGARD !!!

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Daikin VRV 3 pipe changing mode
    By multisync in forum Air Conditioning
    Replies: 23
    Last Post: 22-12-2009, 02:52 PM
  3. Daikin Auto Control Mode
    By InverterMan in forum Air Conditioning
    Replies: 2
    Last Post: 29-10-2009, 05:02 PM
  4. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  5. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •