28-01-2010, 02:03 AM #1
Daikin have heatpump but can not set up auto mode (^_^)
hi, every one !!!
i have an problem that need to be fix in short time .
i am an Engineer from Viet Nam .
i am using remote controller model:BRC1C61 for a VRV3 system which have heat pump mode .
Issue 1: i try to setup it to 'auto' mode but when i press 'OPERATION MODE 'SELECTOR BUTTON ' . It just display 'dry', 'cool', 'heat', 'fan' .i can not find 'auto' mode? what is this problem ...?
Issue 2: In this model can i set up 'max' and 'min' temperature ? please, guide me if it can ... (^_^)
CONGRATULATED THE OUR FORUM ON MORE SUSTAINABLE DEVELOPMENT
Thanks and best regard
-
28-01-2010, 04:23 PM #2
Re: Daikin have heatpump but can not set up auto mode (^_^)
did you say its a 3 pipe system,if its a two pipe system you wont get auto up on the remote
-
28-01-2010, 05:01 PM #3
Re: Daikin have heatpump but can not set up auto mode (^_^)
You need to change field setting on outdoor PCB, mode 3 setting 3 binary 2 this will allow auto change over.
Issue 2: In this model can i set up 'max' and 'min' temperature ? please, guide me if it can ... (^_^)
-
28-01-2010, 05:53 PM #4
Re: Daikin have heatpump but can not set up auto mode (^_^)
You need to change field setting on outdoor PCB, mode 3 setting 3 binary 2 this will allow auto change over.
Hi VRVIII and how are you...?
I know some settings in mode 3... and i don't understand what it mean in your answer, can you please explain more..
Kind regards
cool#9
-
30-01-2010, 12:50 AM #5
Re: Daikin have heatpump but can not set up auto mode (^_^)
don't have any one wanna help me ???
ohh !!!
i really cannot fix this problem , please !!!
"my VRV3 system have 2 pipe , and have both heating ,cooling"
Thank a lot and Kind regard !!!
Have good time , my friends !!!
-
30-01-2010, 04:58 PM #6
-
30-01-2010, 05:22 PM #7
Re: Daikin have heatpump but can not set up auto mode (^_^)
I disagree and think you will find it is possible!
You need to change field setting on outdoor PCB, mode 3 setting 3 binary 2 this will allow auto change over.
Enter setting mode 3 (mode+return for 5secs)
Setting 3 (press set x 3 then return x 1)
enable auto (press set x 1 then return x 2)
exit setting mode (mode x 1)
The controller connected to the heat/cool master indoor will have auto change over available, all others can only change between operation mode of master and fan only.
Last edited by VRVIII; 31-01-2010 at 09:21 AM.
-
31-01-2010, 05:04 PM #8
Re: Daikin have heatpump but can not set up auto mode (^_^)
After you have Auto shown on the remote controller don't you have to set the field code on at the remote to 12-4-x? The final code of x = 1 through 8 for the change over differential between Heating and Cooling. The default factory setting is 1 which is a 0*C differential and each number higher on the setting is 1*C more differential. If you make no change to the field setting then the heating and cooling temps will be maintained the same with a 0*C differential.
-
31-01-2010, 05:29 PM #9
-
01-02-2010, 04:23 AM #10
Ohhh !!! So great
I Fixed my problem to day !!! OH OH !!!
Thank a lot my friends !!!
You are wonderful Engineer !!!
I think our forum will be develop very good !!!
Special thanks to you VRVIII , You are so great !!!
Have a beautiful time and hope we will have more and more discus for advance our knowledge !!!
Finally,
Thank our forum !!!
Thank my friend and best wish !!!
SO GREAT !!!
SO FUN !!!
SO HAPPY !!!
BEST REGARD !!!
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Daikin VRV 3 pipe changing mode
By multisync in forum Air ConditioningReplies: 23Last Post: 22-12-2009, 02:52 PM -
Daikin Auto Control Mode
By InverterMan in forum Air ConditioningReplies: 2Last Post: 29-10-2009, 05:02 PM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM