Thread: room noise
    Nov 2009
    Bangladesh
    room noise
    We just complete a HVAC project.After running the AHU we find a major problems that in few room due to air flow it creating very high level of noise.I thing it is because of very high safety static pressure in the duct, Is there any way to reduce the level of noise in the duct,We used silencer in the duct line,Is there any other reasons which can create sound in the room.
    May 2008
    66
    802
    Re: room noise
    did you check the speed and volume of the air passing the AHU??
    ice
    Nov 2009
    Bangladesh
    Re: room noise
    Yes i checked.it was 5000m3/h,and SP is 2000Pa
    Split Croatia
    6,151
    Re: room noise
    What is air speed on grilles?
    Jan 2010
    Ireland
    Re: room noise
    Hello
    Airborne noise can be generated in ductwork systems
    as a result of excessive air velcoities.
    If noise is emitted from the distribution ductwork, and the duct air velocity exceeds the recommended maximum levels, you could have a major problem.
    You could consider the following options;
    1. lag the duct with acoustic insulation - however retrofitting acoustic insulation has a limited effect.
    2. integrate acoustic insulation with ceiling system-it should help dampen breakout noise.
    3. measure the air flow rate at duct sections that are audible from within the occupied space - check measured air volumes against design and commissioning data, reduce if possible.
    If problem noise is occuring at the supply air terminal's, measure the face velocity.
    Typically, the maximum recommended face velocity for louvre faced diffucers, serving general open plan office area should not exceed c. 2.5m/s -so as to satisfy best practice room noise levels.
    Rather me than you.
  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Last Post: 09-08-2010, 12:10 PM
  2. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Last Post: 13-03-2009, 01:49 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Last Post: 28-05-2008, 01:08 AM
  4. Thawing Room (defrosting Room For Meat)
    By arunuae in forum Commercial
    Last Post: 09-02-2008, 09:24 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Last Post: 22-04-2005, 05:58 AM