    Daikin star wired



    Could a star wired vrv heat recovery cause transmission faults after 3yrs of being trouble free?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Daikin star wired

    Star or Y wired is about the motor only, regardless to the work it is doing.

    Its easier on the motor start torque and pulls less amps then Delta or Δ.

    And To your question, nope.

  3. #3
    Join Date
    Jan 2010
    Location
    Leeds
    Age
    44
    Posts
    18
    Rep Power
    0

    Re: Daikin star wired

    Quote Originally Posted by ICEmarc View Post
    Could a star wired vrv heat recovery cause transmission faults after 3yrs of being trouble free?
    Hi Marc
    Do you mean a VRV system wired in a way other than a 'daisy chain' style.
    Where you have wiring randomly connected between indoor units and not in sequence?

  4. #4
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Daikin star wired

    Strange enough, I would say yes.
    I had a 'K' series operating for years which was hooked up to a DBACS. This VRV was added at a later date and the F1/F2 loop was star wired into the DBACS panel as opposed to connecting up to the rest of the daisy chain.
    Did get the odd fault appearing but it always reset. In the end I just rewired.

    Jase

  5. #5
    Join Date
    Apr 2009
    Location
    UK
    Posts
    21
    Rep Power
    0

    Re: Daikin star wired

    Quote Originally Posted by CraigMac0113 View Post
    Hi Marc
    Do you mean a VRV system wired in a way other than a 'daisy chain' style.
    Where you have wiring randomly connected between indoor units and not in sequence?
    Exactly what I mean, I have a vrv ii heat recovery system thats been working fine but now keeps going into U9, the wiring is appauling and I'm going to trace it tommorow. If 1 fan coil was isolated by the customer would it create a transmission fault?

    Quote Originally Posted by Jase View Post
    Strange enough, I would say yes.
    I had a 'K' series operating for years which was hooked up to a DBACS. This VRV was added at a later date and the F1/F2 loop was star wired into the DBACS panel as opposed to connecting up to the rest of the daisy chain.
    Did get the odd fault appearing but it always reset. In the end I just rewired.

    Jase
    Only just taken over maintenance of this system but client states it's never happened before

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Daikin star wired

    Quote Originally Posted by chemi-cool View Post
    Star or Y wired is about the motor only, regardless to the work it is doing.

    Its easier on the motor start torque and pulls less amps then Delta or Δ.

    And To your question, nope.
    Chemi

    This is related to the wiring of the VRV indoor units for the comms wiring. It is supposed to be daisy chained from one to the next to the last. Occasionally for whatever they wire to a central point and 'star' out like spokes on a wheel to each indoor unit.

    although Nike has an interesting comment

    http://www.refrigeration-engineer.co...ead.php?t=3966

    page 174 as nike suggests
    http://www.daikinac.com/commercial/d...SiUS39-504.pdf

  7. #7
    Join Date
    Jan 2009
    Location
    london
    Posts
    52
    Rep Power
    16

    Re: Daikin star wired

    Hi Guys,

    In my opinion a U9 fault is generally a transmission error, where one unit has powered down or turned off for some reason. All of the remotes will show U9, which is basically telling you that another unit on the system is in fault.

    As to the way the wiring is run, I too was told that it works on resistence of the cable, but then I spoke to daikin technical and was told that it works on what order the indoor pcbs, simply, reply.
    Normally any centralised contoller has to be connected to the outdoor, But I know that, on a two pipe system, you can star off of any indoor unit. But if that unit powers down for any reason a fault will occur.
    Also I read on the link that was pasted on this tread, that when an addition is added to a vrv or replacement pcb, it will all need re addressing, this is not totally true. If the system has higher form of control i.e centralised controller. The units will not lose their address , you would only have to give any new unit a spare address and re-set system. It does not autmatically re-address. A system will only automatically re address if no higher control is connected to the system.
    All of this infomation, I belive to be correct, as from daikin technical
    Hopes this helps Troy

  8. #8
    Join Date
    Apr 2009
    Location
    UK
    Posts
    21
    Rep Power
    0

    Re: Daikin star wired

    Quote Originally Posted by troymedhurst View Post
    Hi Guys,

    In my opinion a U9 fault is generally a transmission error, where one unit has powered down or turned off for some reason. All of the remotes will show U9, which is basically telling you that another unit on the system is in fault.

    As to the way the wiring is run, I too was told that it works on resistence of the cable, but then I spoke to daikin technical and was told that it works on what order the indoor pcbs, simply, reply.
    Normally any centralised contoller has to be connected to the outdoor, But I know that, on a two pipe system, you can star off of any indoor unit. But if that unit powers down for any reason a fault will occur.
    Also I read on the link that was pasted on this tread, that when an addition is added to a vrv or replacement pcb, it will all need re addressing, this is not totally true. If the system has higher form of control i.e centralised controller. The units will not lose their address , you would only have to give any new unit a spare address and re-set system. It does not autmatically re-address. A system will only automatically re address if no higher control is connected to the system.
    All of this infomation, I belive to be correct, as from daikin technical
    Hopes this helps Troy
    U9 fault was indeed an isolated indoor unit thanks for pointing me in the right direction

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Daikin star wired

    Thanks Rich,
    I know I did a good thing when I've stopped touching those air conditioners years ago.

    I was referring to regular electric motors with or without frequency controller.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Daikin Hard wired controller
    By marc5180 in forum Air Conditioning
    Replies: 16
    Last Post: 10-11-2007, 06:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •