    copeland scroll



    I have a new copeland compressor the I believe has just seized. It has been running for about 4 weeks. If pulls about 70 amps. the head pressure is 100 when off. when I apply power it jumps to 110 then stop. l Suction pressure does not change. What would cause it to go out so quickly?



  2. #2
    Join Date
    Mar 2008
    Location
    United Kingdom
    Posts
    51
    Rep Power
    17

    Re: copeland scroll

    What is the compressor running?
    Is it on a condensing unit or is it part of a pack system?
    Has the system been in for while?
    Is the compressor located higher than the the evapourator?
    Does it have an oil seperator fitted?
    What refrigerant is it on?
    This would be a start so that we can build a picture of the system before attempting to fault find it.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: copeland scroll

    I see that you are a student.

    Is this a course question or a site situation?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: copeland scroll

    In that application you have the compressor pump heat or air conditioning

  5. #5
    Join Date
    Jan 2010
    Location
    usa
    Posts
    16
    Rep Power
    0

    Re: copeland scroll

    Brain_UK: It is an actual unit. I am a student getting my Masters of Research. A/c is a side I like to do. There is a lot to learn in a/c, and I love to learn.

    andywill: The compressor is running a 5-ton gibson a/c unit.
    It is a split system.
    The system was newly installed 4 weeks ago. compressor is under warranty. but will it go out agian if I just replace it. I like to find the cause of the problem. It is part of learning.
    The compressor is lower the the evaporator.
    I would have to say that it does not have an oil separator because I don't know what one looks like and I did not install one.
    The unit is running r-22.

    Would an oil separator help?
    Would an accumulator help?

    Reason for asking is I read that small amounts of liquid running through a compressor will take the oil with it. And I was wonder if this could have been the case.
    Also am I right in thinking that the compressor as seized or could it be something else.
    Thanks for taking the time to respond.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: copeland scroll

    Quote Originally Posted by jakehabing View Post
    I have a new copeland compressor the I believe has just seized. It has been running for about 4 weeks.
    Did it run properly for four weeks?

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: copeland scroll

    Quote Originally Posted by jakehabing View Post
    Brain_UK: It is an actual unit. I am a student getting my Masters of Research. A/c is a side I like to do. There is a lot to learn in a/c, and I love to learn.
    Start here:

    http://www.refrigeration-engineer.co...ad.php?t=19701

  8. #8
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    9
    Rep Power
    0

    Re: copeland scroll

    Single Phase or Three Phase?

  9. #9
    Join Date
    Jan 2010
    Location
    usa
    Posts
    16
    Rep Power
    0

    Re: copeland scroll

    Gary,
    It seemed to run fine for the four weeks then one morning I check on the unit and the compressor was not running, it was warm. It had pulled so much power that it melted some insulation on a wire and blew a 30amp fuse. I checked the to see if the compressor had shorted to ground and it had not.

    JHdlinc,

    It is Single phase

  10. #10
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: copeland scroll

    hi check your phase sequence this sounds like an electrical problem that turned mechanical ,a scroll could run reverse direction but not for long a phase sequence relay would prevent this