18-01-2010, 08:57 PM #1
R134a Help!!
Got a little test rig coldroom at work to train on.
Supervisor asked me to do home work
I got to find out what to set the HP and LP up at
Would any one know? the refrigerant is 134a
He told me to keep in mind its a pump down system
Thanks
-
18-01-2010, 09:27 PM #2
Re: R134a Help!!
I'd set the hp switch for 60-65c condensing temperatue, you will need to convert this to a pressure with a slide rule or pt chart.
The lp setting would depend on the design temperature of the cold room and the type of compressor.
For a recip comp, i'd set the cut out at 2 or 3psi for a scroll it would possibly be higher.
For the cut in you need to convert the design temperature of the room e.g. 12c into a pressure with you slide rule pt chart and make the cut in a few psi lower, maybe 5 or 10 psi.
What you want it a nice wide differential to stop short cycling with a high enough cut out that it doesn't go into a vacuum and a low enough cut in that it will cut back in. If the cut in is too high the tev can limit the suction pressure to below the cut in pressure and you unit won't start till the room is too warm. This is more of an issue with pumpdown cut out.
Jon
-
18-01-2010, 09:50 PM #3
-
18-01-2010, 10:26 PM #4
-
18-01-2010, 11:15 PM #5
Re: R134a Help!!
lots of space on the reverse side of a p/t chart
Similar Threads
-
R507 in an R134a compressor: any danger?
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 21-12-2009, 12:44 AM -
Clogged condenser leading to no gas on R134a systems?
By runningonavac in forum RefrigerantsReplies: 12Last Post: 01-09-2009, 10:52 PM -
r12 vs r134a minifridges (efficiency)
By ziddey in forum FundamentalsReplies: 10Last Post: 25-06-2009, 06:26 AM -
Pressure Transmitter R134a Setpoints
By cooltrain in forum Technical SpeculationsReplies: 0Last Post: 28-02-2005, 09:05 AM -
Is there anything about R134a that is better than R12?
By dude in forum RefrigerantsReplies: 5Last Post: 01-03-2004, 09:59 PM