    DX capacity lower than condensing unit



    I have DX unit which capacity 30.8 Kw install with condensing unit which capacity 39.3 Kw . DX capacity lower than condensing unit , Is this a problem ?? What's this problem ?? How can repair this problem ?



  2. #2
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: DX capacity lower than condensing unit

    Suction pressure & evap temp may be lower than DX coil design conditions, resulting in excessive dehumidification.
    One way to resolve this is by fitting an EPR.

    What are the rating conditions for the condensing unit?
    Is it possible that the condensing unit has been selected to match the evap at a higher amibient (and SCT)?
    Does the condensing unit have any capacity control?

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: DX capacity lower than condensing unit

    Hi M.Saleh.
    Depending on the design selection of evaporator and compressor conditions. Most manufacturers of evaps state performance for say a freezer coil at 4'C diff between air on and evaporating temps. Add to that the suction line losses bends accumulators valves crankcase regulators, the compressor suction will be /could be 6 'C lower, for a balance to evap., capacity.
    So if you compare an evap duty at -18 'C room temp and at compressor duty of -18'C the Kw /HP could be hugely different to evaporator. To compound problem design engineer could have selected a bigger evap TD at say 6.0 'C.
    So there goes a comparison imbalance.
    magoo.
    Last edited by Magoo; 18-01-2010 at 03:02 AM. Reason: spelling

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. Condensing Unit
    By marksmith970 in forum Commercial
    Replies: 4
    Last Post: 13-08-2008, 10:17 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •