LG split system fan cont. trouble shooting
I hoping to be helped with an LG split system model LS-K2463HL the evap. fan cuts out for a few seconds, then starts again. Is there a self diagnosis function or a reset proceedure for the fan speed control module? The fan speed varies when set on a set speed, other than that it is operating fine.
Any suggestions?
-
14-10-2004, 04:44 PM #2
Re: LG split system fan cont. trouble shooting
How's the capacitor? See that it is within about 10% of the rating and check that there is no continuity from the pins to the casing of the cap!
Just a suggestion.
-
14-10-2004, 06:30 PM #3
Re: LG split system fan cont. trouble shooting
Are you aware if the "Chaos Swing" function on lg units ?
Seriously, they have a setting, said to mimic a fresh air breeze.
This is done by randomly moving the louvres and altering the fan speed.
I can't remember which button it is on the controller, but one of them will switch it off.
This is not a wind up, and it could be the cure to your problem.
cheers
eggs
-
17-10-2004, 12:39 PM #4
Re: LG split system fan cont. trouble shooting
Thanks, I am aware of the Chaos program and it is not this. It is as if the programing for the fan speed control has gone haywire. It only happens on heat which is ok as its now coming into summer. Ill probably sort it next year in the cooler months.
-
17-10-2004, 02:12 PM #5
Re: LG split system fan cont. trouble shooting
If it only happens on heating mode then look closely at the coil sensor. This holds the fan off until the coil is up to temp so that cold draughts are not blown around the room. Faulty connection springs to mind
-
03-06-2009, 08:43 AM #6
-
05-06-2009, 06:11 PM #7
Re: LG split system fan cont. trouble shooting
hi ianv if you have access to internet, lol go to lg multi codes or similar and download codes, it will give you hints
LG Air Conditioning Universal & Multi Split Fault Codes Sheet
-
05-06-2009, 07:12 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: LG split system fan cont. trouble shooting
You probably have refrigerant leak. Find technician which will recover and weigh refrigerant amount in system and if it is lower than on nameplate, or if you have excessive pipe length. Than, if refrigerant is lower amount than necessary, he need to find and repair where it is leaked or charge additional refrigerant if pipes are longer than it is unit pre-charged for.
-
07-06-2009, 04:46 AM #9
Re: LG split system fan cont. trouble shooting
thanks fellas, i have it fixed, a new PC board and alls ok, it looks like it may be a common prob however bods not knowing how it should operate accept the problem as normal.
alls well for now.
oh and the high wind problem mentioned may be that the fan needs cleaning. i did it when i had the evap unit apart and it is much quieter now.
Thanks for the input.
Ianv
-
01-02-2011, 03:31 PM #10
Re: LG split system fan cont. trouble shooting
its normal if you put on auto mode for blower fan.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
York chiller system trouble shoot
By lawrence7435 in forum Trouble ShootingReplies: 4Last Post: 06-03-2007, 06:54 PM -
can a r22 split system condensing unit be used to cool a display fridge
By tsangep in forum RefrigerantsReplies: 8Last Post: 20-05-2006, 04:21 PM -
Trouble Shooting
By Vincent Yu in forum FundamentalsReplies: 20Last Post: 22-11-2005, 02:04 PM