    Smile problem with DAIKIN FCQ 71 > i need technical book



    good morning

    i search technical book for

    cassette type FCQ 71 C7 VEB
    sérial number 2918602

    groupe compresseur RQ 71 B2 V3B,
    sérial number J 000 104

    in cooling mode , by the time the system stops, the LED defrost flashe (cold operation is no defrost normally) the remote stops responding.

    thanks for wour answer



  2. #2
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: problem with DAIKIN FCQ 71 > i need technical book

    If you are in cooling and the outdoor unit stops about every 10 minutes you will probably find that the indoor units coil tenperature is dropping below -3 and the outdoor unit is going into frost protection. If this is a communication room, you may have this problem due to low humidity. Because you are using a fixed speed compressor the control is limited. An inverter is better for this type of application. You can input a field setting on the indoor unit and I think with that unit you can turn on dip switch 3 on the second set of dip switches which should be the setting for low latent heat applications. Check your coil temperatures in code 41 also.

  3. #3
    Join Date
    Sep 2009
    Location
    PARIS - FRANCE
    Age
    72
    Posts
    12
    Rep Power
    0

    Wink Re: problem with DAIKIN FCQ 71 > i need technical book

    good evening BRUNSTAR ,

    thanks for your post

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: problem with DAIKIN FCQ 71 > i need technical book

    Quote Originally Posted by mimifrigo View Post
    good evening BRUNSTAR ,

    thanks for your post
    not a problem, let us know how you go with that one.
    jes suis a paris en ce moment,, bonne annee

  5. #5
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: problem with DAIKIN FCQ 71 > i need technical book

    Quote Originally Posted by mimifrigo View Post
    good morning

    i search technical book for

    cassette type FCQ 71 C7 VEB
    sérial number 2918602

    groupe compresseur RQ 71 B2 V3B,
    sérial number J 000 104

    in cooling mode , by the time the system stops, the LED defrost flashe (cold operation is no defrost normally) the remote stops responding.

    thanks for wour answer
    Brunster,

    Do you not think this sounds more like the units has an infra red controller option installed, with defrost LED flashing on the receiver.

  6. #6
    Join Date
    Sep 2009
    Location
    PARIS - FRANCE
    Age
    72
    Posts
    12
    Rep Power
    0

    Re: problem with DAIKIN FCQ 71 > i need technical book

    good evening

    yes , infra red controller option is installed

    happy new year !!

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: problem with DAIKIN FCQ 71 > i need technical book

    are you sure it is not the operation led that is flashing and the unit is under fault conditions?
    are you sure it is not the timer light that is on?
    does the unit start back up by itself or do you have to reset the power to the unit for it to start again?

    If it is the operation led flashing you can get a fault code from the controller.

    Is the infra red controller newly installed?
    If it is it could be an incorrect reciever or The other thing that you could check is the dip switch on the back of the controller to make sure it is set to master.
    You could try wiring a hard wired controller to the system to see what is going on.

  8. #8
    Join Date
    Sep 2009
    Location
    PARIS - FRANCE
    Age
    72
    Posts
    12
    Rep Power
    0

    Re: problem with DAIKIN FCQ 71 > i need technical book

    hello brunstar ,
    thank for your answer .
    Now , the machine run in heating mode and it is ok . These problems are arrived in the end of summer in cooling mode . after reset it was restart but i have not look the défault before restart . i made install in october and i think the problem come back in next heat season .i am surprise that Daikin hot line cannot say to me the reason of the flashing lamp defrost

    good day

Similar Threads

  1. Problem with a Daikin Compressor - Please help!
    By Brandon3131 in forum Air Conditioning
    Replies: 10
    Last Post: 26-08-2009, 01:42 AM
  2. Daikin going to pot?
    By Clk320_Greg in forum Air Conditioning
    Replies: 16
    Last Post: 19-07-2009, 06:03 PM
  3. daikin controllers
    By declan simmonds in forum Air Conditioning
    Replies: 25
    Last Post: 10-07-2009, 10:54 PM
  4. Daikin split problem (any ideas)
    By airconjohn in forum Air Conditioning
    Replies: 14
    Last Post: 17-02-2008, 08:40 PM
  5. daikin technical website
    By freezy in forum Air Conditioning
    Replies: 4
    Last Post: 21-03-2005, 05:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •