    Problems in r22 chiller design
    I have designed a chiller and I am facing problems with low suction pressure
    The design conditions are
    Medium - Water
    Refrigerant - R-22
    Water inlet temp - +11ºC
    Water outlet temp - +6ºC
    Evaporating temp - +1ºC
    Chiller design: Type DX Chiller, Double circuit
    Tube OD: 3/4", 20 Gauge plain copper tubes
    Tube Length: 12 Ft
    No of tubes:380 Nos
    No of pass (refrigerant side):6 Pass (per Circuit)
    No of Pass (Water side):22 Pass
    No of tubes per pass:
    1st pass: 9+9
    2nd pass: 14+14
    3rd pass: 28+28
    4th pass: 31+31
    5th pass: 52+52
    6th pass: 56+56
    The above chiller is designed for 135 TR Capacity, but I am unable to get the desired capacity.
    The suction pressure is very low (Between 2.8 to 3 Kg/Sq Cm) at 6ºC chiller outlet
    The chilled water flow through chiller is 90 Cu mtrs/hr
    Temp diff across the chiller is not more than 3.5ºC
    I request somebody to comment on this and suggest the remedy
    Umesh
    Jun 2001
    N.Ireland
    1,630
    Re: Problems in r22 chiller design
    Hi umesh
    what pressures and temperatures are you measuring?
    Full log please.
    Kind Regards Andy
    Sep 2003
    ISRAEL
    72
    4,248
    You also have to check the water flow and water pressure drop on the heat exchanger.
    You might have a too small pump.
    fridgy's Avatar
    fridgy Guest
    Quote Originally Posted by chemi-cool View Post
    it could also be the flow rate is too high. not enough dwell time in the evaporator will affect the heat absorbtion, i.e lowering the suction pressure and not achieving a good split. try slowing the CHW pump or restricting the flow to see if it makes a difference. good luck
    Aug 2007
    42
    135
    Is it me or does that sound like a lot of passes for a chiller? Your expansion valve would have to be very good to cope with all conditions on a 6 pass chiller circuit. I would suggest a 2 or 3 pass circuit and check your valve sizing.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?
    38
    'What is the TX valve superheat?
    magoo
    May 2006
    India
    399
    Calculated flow on the 135 tr is 83.7 m cub per hour .
    1) probably flow appears to be high v/s design i.e. 90 m cub per hr .
    2) chiller pump heat load is accounted in the design load calculations ?
    3) liquid temp aproaching tex ?
    4) temp at tex bulb ?
    5) temp at comp suction ? High suction superheat .
    6) pr drop in tex valve distributor ?
    7) what is condensing temp ?
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Thumbs down Re: Problems in r22 chiller design
    very intresting subject,but this first poster do not react!no manners.
    Moideen-Dubai
    TitanioMan's Avatar
    TitanioMan Guest
    Hello Umesh
    from my point of vew
    you do have a lot potential to do your needs with the chiller units, lot of area and tube arrange is OK, on DX chillers the unit is really 1 pass only on water side with maybe 22 buffles (looks a lot for me), this can cause a lot of pressure drop and reduce water velocity contact on tube face (the heat exchange rate is proportional to this velocity), you need to increase suction pressure with more liquid thrue TXV valve and set to 0 °, if you are using pure water do not operate chiller below -1 (3.5 to 3.8 BarG), revise the actual superheat and with temperature you can find if some ice is building inside or need more refrigerant, the ice cause heat transfer deficience
    Oct 2006
    Mumbai
    64
    5
    Hello everybody
    First of all I am very sorry for not replying to your posts, as I was unwell and hospatilized, sorry Mr Moideen.
    Firstly as replied by Hall engineer UK, pl clarify why I have to go for 2 to 3 pass, instead of 6 pass, will it not cause reduction in the per tube velicity and accumulation of oil?
    As mentioned by Mr. DD Koranne, the recommended flow rate by him, of 83.7 cu m /Hr, will cause the temperature difference across of the chiller will increase, the total capacity will not change.
    I have tried setting the expansion valve as suggested by titanio man but there is no change in the suction pressure.
    My problem is the temperature difference is only upto 3.5ºC across the chiller and the suction pressure is not increasing, it goes upto 2.5ºC
    I am unable to understand the proble, as I am not getting the required capacity
    Umesh Pradhan
  1. York Chiller problems
    By ingherrera in forum Commercial
    Last Post: 26-07-2011, 03:10 PM
  2. york chiller ylcs control logic problems
    By koolkatz in forum Trouble Shooting
    Last Post: 04-12-2009, 11:59 AM
  3. chiller problems
    By iceman6869 in forum Technical Discussions
    Last Post: 19-11-2009, 07:47 AM
  4. Propylene Chiller Problems
    By Maintenance Man in forum Fundamentals
    Last Post: 23-09-2009, 11:50 AM