    Dec 2005
    uae
    54
    Question York YDAJ gsi reciprocating chillers
    York YDAJ gsi chiller display system hanged. no any button functioning, and cannot getting any information.(chiller is working properly)
    Display board replaced and checked, but the situation is still the same. Pl give a solution.
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Thumbs up Re: York YDAJ gsi reciprocating chillers
    Quote Originally Posted by vinod View Post
    check ribbon cable which connecting display board to processor board.replace that.
    expecting your response
    Moideen-dubai
    Dec 2005
    uae
    54
    Ribbon and display board replaced. but still the same situation
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    it might be the trouble of Power supply board.check the voltage from power supply board J3 terminal,it should be 12VDC healthy.and also check the J1,J6 terminal from processor board,wire loose or misplaced.
    Moideen-Dubai
    ireland
    1,453
    i think there should also be a 5vdc test point on the board, check this also. This problem can(although rare) be caused by a faulty transducer or sensor.
    al
    70
    4,702
    47
    To add to the above excellent advise!
    Check if the control panel emergency stop device. Or any remote emergency stop devices are off?
    Dec 2005
    uae
    54
    The problem solved by replace the key pad. Thanks to all.
  1. York Chillers
    By N.Lewis in forum Air Conditioning
    Last Post: 17-11-2010, 07:36 PM
  2. centrifugal chillers york
    By Magic in forum Technical Discussions
    Last Post: 12-11-2009, 06:08 PM
  3. York & Trane Reciprocating Chiller
    By Gigas in forum Air Conditioning
    Last Post: 21-05-2008, 12:21 AM
  4. York Millennium Chillers
    By shairgr in forum Industrial
    Last Post: 10-12-2007, 03:04 PM
  5. York Reciprocating Compressor
    By lldelfin67 in forum Industrial Compressors
    Last Post: 17-07-2007, 03:56 PM