Fujita E3 fault
Hi Does anyone know what a E3 fault is on a Fujita ASW-H24B4/HS 7Kw high wall split. I know it should be replaced but if we can get it going for the tenant we will.
thanks Darren
-
31-12-2009, 12:34 PM #2
Re: Fujita E3 fault
Hello.
It should be the sensor in front of the indoor coil ("room sensor") short circuited - it should be replaced. As you probably would not find now a replacement, it is possible to "imitate" the sensor by a resistor (cut it off and connect a resistor instead) - so long as the new sensor is found.
Only the A/C will work constantly as there will be no temp control - so it will be necessary to switch the A/C off and on from time to time manually.
-
01-01-2010, 01:58 AM #3
Re: Fujita E3 fault
Hi,
You can download the manual for these if you google search,,,bigwarehouse
-
01-01-2010, 08:33 AM #4
-
03-01-2010, 07:58 PM #5
Re: Fujita E3 fault
Thanks for the information everyone it has been a great help.We will go to site today and look at the unit and I will post how we went.
-
04-01-2010, 12:12 PM #6
Re: Fujita E3 fault
Thanks everyone for the help with the fault code information. It was the return air thermistor and after changing it with another sensor made up from spares it worked. So once again thanks
Similar Threads
-
YORK YAEP recip chiller fault
By chiller1 in forum Trouble ShootingReplies: 8Last Post: 04-06-2010, 10:41 AM -
Beer Troubleshooting
By nike123 in forum Chit Chat & Service StoriesReplies: 3Last Post: 29-04-2008, 10:15 PM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 10:23 PM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM