    Airedale low pressure fault



    Hi Guys,
    Hope one of you can help. I`ve got a problem with an Airedale CHS6 that trips on LP (1bar) in heating mode. Ambient`s -1c at the moment. It runs for about three seconds then goes out on LP, as there was no time to take any temperatures or accurate pressures I thought it easiest to remove and weigh the correct amount of refrigerant in as I had found a very small leak beforehand. Alas no joy, it`s still tripping. The pressure after the filter on the return line from the indoor unit (in heat mode remember) at tripping is about 5bar and rising, and after the TXV and reversing valve 1bar. Now here`s my thoughts: Am I`m looking at a faulty TXV? (no difference if I hold the bulb in my hand) I`m hoping it`s not a duff reversing valve as that`s going to be a pig to get to.
    What do you think guys?
    A virtual Xmas drink`s on me for the one that comes up with the answer....sod the expense, drinks all round!



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Airedale low pressure fault

    Outdoor fan is OK and spinning at full speed?

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Airedale low pressure fault

    Hi Nike,
    Thanks for the quick reply,
    The fan doesn`t get a chance to run as unit trips after three seconds or so, that`s why I think it could be a restriction in the suction line. However, as it runs for such a short time I can`t take any accurate readings.
    By the way, it ran ok when was last on site ( not working on this unit then, just happened to notice it running ok)when the ambient wasn`t so low so I think there was just enough refrigerant flow to keep it from tripping. Now the ambient`s dropped that may not now be the case.

    Thanks again Nike

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Airedale low pressure fault

    At -1°C ambient i would expect much higher evaporation and it is certain that you have some restriction at suction side (when heating).
    It is probably not reversing valve or compressor since you have good compression ratio.
    I would try to run cooling mode and see if the problem is still there and that would help in locating where is restriction.

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Airedale low pressure fault

    I had another look today and did what nike suggested and ran in cooling mode, problem still remaining.
    Turned the unit back to heating mode.
    I fitted a line tap valve between the outdoor condensor and the reversing valve to measure the pressure, here`s what I found: 5 bar approx before the valve and dropping to .5 bar and tripping after the valve on the suction into the compressor.
    I`d have thought the pressure before the valve should be simmilar to after the valve. But hey, this is what this forums for, to pick wiser brains than mine.
    Now, I reckon I`m looking at a u/s reversing valve but I just want to see if any of you have come across this before I change said valve as this job looks a right pig to do.

    Cheers guys

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Airedale low pressure fault

    Yepp, shouldn't see any pressure drop across the reversing valve (Assuming that you look at the right pipes)

    Before you change the reversing valve, try to gently tap it on the end with a hammer.
    These valves have a 'floating' piston inside them that is operated by pressure and any debris in the system will cause the piston to get stuck.
    If you are lucky a gentle tap will free the piston and give you time to schedule a proper repair/clean up.

    Good luck

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

Similar Threads

  1. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2007, 01:06 PM
  4. Replies: 27
    Last Post: 27-10-2006, 03:19 AM
  5. screw compressor
    By vinod in forum Trouble Shooting
    Replies: 9
    Last Post: 17-12-2005, 01:46 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •