    Mitsubishi Mnet transmission cable question



    I would like to ask, can I use control cable -Belden 8760 to connect between outdoor unit and Mnet?



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi Mnet transmission cable question

    No
    Cable size is too small at 0.8mm.

    Mitsubishi specification is 2 core screen 1.25mm.
    In UK this is non standard size so we use 1.5mm.

    If you use smaller section cable you can get all sorts of communication problems & end up replacing it all with the correct type cable.