15-11-2009, 03:37 AM #1
whats the max/min temp differential allowed
before calling a mechanic thermostat deffective?
i have one that set at 40ºF will keep the unit working till 32ºF and will start back at 70ºF
I'm sure that is not normal so i opened the thermostat and everything seems to be ok.
i checked it was placed, exactly in the same place and way before unmounting it and the conections are correct.
it's a danfoss thermostat like one of these...
sorry if you find this post irrelevant but i could use a hint as to if these can be recalibtated or disposed for new ones.
thanks in advance
-
15-11-2009, 08:00 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: whats the max/min temp differential allowed
2 to 3 K is normal termostat differential for air conditioning applications.
For particular termostat you should found its technical literature, since differential depend on his usage field.
-
15-11-2009, 01:06 PM #3
Re: whats the max/min temp differential allowed
Apart from changing to an electronic control, Eliwell, Dixell etc., is the sensing bulb in good contact to the fluid being sensed?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-11-2009, 02:09 PM #4
Re: whats the max/min temp differential allowed
If it worked before and now doesn't, technicaly its broked and needs a new one.
-
15-11-2009, 08:38 PM #5
Re: whats the max/min temp differential allowed
ok so either the thermostat is broken (because it does not work as it used to) or I reinstalled the temperature bulb incorrectly.
the thermostat as nike ponts out has a 3K differential and i placed the copper bullet at the air return side of the evaporator coil, where i found it in the first place, where should i place the temperature bulb to get the accurate measuring and prevent extended runtimes?
thanks
-
26-11-2009, 03:29 PM #6
Re: whats the max/min temp differential allowed
hi frostedflake, I seam to remember somthing about setting up the stat < file < it has to point downwards or the alchol or liquid inside the <file< migrates along the cappilary making the stat uncontrolable, also I remember there is a manual setting to give a max + min temp range,
-
24-02-2011, 02:46 PM #7
Re: whats the max/min temp differential allowed
thanks for the help
Similar Threads
-
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
19XL High Discharge Temp intermittent alarm at compressor start
By pete_d in forum CommercialReplies: 5Last Post: 08-11-2009, 05:10 PM -
Temp. Rise at duct outlet
By jwasir in forum Trouble ShootingReplies: 13Last Post: 10-05-2008, 04:22 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
cold room temp & the product temp
By smpsmp45 in forum NH3Replies: 9Last Post: 21-09-2007, 11:46 PM