Quote:
Originally Posted by kathir
dear all...
please guide me to select a fan for a ventilation system.ie. fan selection,static pressure,rpm,cfm calcuations...etc
regards/kathir
I don't know if the best book on air side design is still in print but do try and locate a copy of "WOODS practical guide to fan engineering", it will not matter if it is OLD fan laws do not change.
The definition of a fan is a "machine which propels air continuously by aerodynamic action"
There are three basic types of fans, centrifugal, propeller and axial.
All three are selected for different types of applications the major selection criteria being external resistance, noise etc.
Fan Laws.
With constant impeller size
1. Volume flow varies directly as speed of rotation
2. Pressure developed varies as (speed of rotation)2
3. bhp absorbed varies as (speed of rotation)3
With constant speed of rotation
4. Volume flow varies a (impeller size)3
5. Pressure developed varies as (impeller size)2
6. bhp absorbed varies as (impeller size)5
Consequently with varying speed of rotation and impeller size
7. Volume flow varies as (speed of rotation) x (impeller size)3
8. Pressure developed varies as (speed of rotation)2 x (impeller size)2
9. bhp absorbed varies as (speed of rotation)2 x (impeller size)5
I am sorry that the system does not allow the (squared 2) or the (cubed 3) etc. to be put in the correct location ie against the bracket above the base line.
To answer your original question, first you have to determine the air volume required to ventilate the space under consideration. The next phase of selection requires a calculation of the air distribution system, ductwork, grilles, diffusers etc. to provide an assessment of the anticipated external resistance to air flow the fan will have to over come to deliver the calculated air volume.
The type of fan would be selected based on the type of application, for example an axial 2 pole would be acceptable in an industrial application but due to the noise generated a centrifugal would be more appropriate for commercial and residential ventilation systems.
I hope some of this helps.